The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm² flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (crselectric, mbhydro), 232 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89645 - 10/12/04 01:32 PM Maximum Load on 15A
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Is it not required to limit the load on a 15A breaker? I have a 11A load on a Condensing Unit that is being fed by a 15A brkr...I am thinking this is too small.

Any replies will be greatly appreciated.

regards

mustang
_________________________
Electricity has no respect for ignorance!

Top
2014 / 2011 NEC & Related Books and Study Guides
#89646 - 10/12/04 01:37 PM Re: Maximum Load on 15A
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
A 15 amp breaker is allowed to be loaded 100% up to 3 hours, longer than 3 hours the load may only be 80% which is 12 amps.

11 amps on a 15 amp breaker is fine.

However you said this is a condensing unit, the label should say what size overcurrent protection to use.



[This message has been edited by iwire (edited 10-12-2004).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89647 - 10/15/04 04:42 PM Re: Maximum Load on 15A
Steve T Offline
Member

Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
The breaker for a condenser is only short-circuit protection which can be 175% of the rated load current or branch circuit selection current, whichever is greater. If that's not enough to allow the compressor to start then you can go up to 225%. 11x1.75=19.25 an 11X2.25=24.75.

Top
#89648 - 10/16/04 10:28 AM Re: Maximum Load on 15A
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Steve: I agree with Bob on this. I typically just apply
 Quote:
440.22(C) Protective Device Rating Not to Exceed the Manufacturer’s Values. Where maximum protective device ratings shown on a manufacturer’s overload relay table for use with a motor controller are less than the rating or setting selected in accordance with 440.22(A) and (B), the protective device rating shall not exceed the manufacturer’s values marked on the equipment.


Not that the math is that difficult, but in my opinion, why go through it?
_________________________
Ryan Jackson,
Salt Lake City

Top
#89649 - 10/16/04 10:37 AM Re: Maximum Load on 15A
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
You can not "do the math" you must use the Manufacturer’s Values.

Anything higher than that and you have tossed out the UL listing.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89650 - 10/16/04 10:52 AM Re: Maximum Load on 15A
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
That too
_________________________
Ryan Jackson,
Salt Lake City

Top
#89651 - 10/16/04 02:04 PM Re: Maximum Load on 15A
SteveMc Offline
Member

Registered: 02/05/04
Posts: 61
Loc: Rock Hill, SC
#14 awg wire ok?

Top
#89652 - 10/17/04 10:11 AM Re: Maximum Load on 15A
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Absolutley #14 is OK. If the load is 11 amps, all you need is a conductor that satisfies the load. You can then put on the highest fuse or breaker allowed by the manufacturer and still be OK. For example, if the load was 11 amps and the nameplate says maximum OCPD is 40 amps, you may install a 40 amp breaker and run #14 for the circuit.

See 240.4(D) which points you to 240.4(G), then go to part IIIof article 440 for A/C units.

 Quote:
III. Branch-Circuit Short-Circuit and Ground-Fault Protection
440.21 General.
The provisions of Part III specify devices intended to protect the branch-circuit conductors, control apparatus, and motors in circuits supplying hermetic refrigerant motor-compressors against overcurrent due to short circuits and grounds. They are in addition to or amendatory of the provisions of Article 240.
_________________________
Ryan Jackson,
Salt Lake City

Top