The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 21
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89574 - 10/09/04 03:13 AM Multiwire Branch Circuit with Unequal OCP
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I am currently remodeling office space, I have an existing 8/3 AC cable that runs from a panel 125' to a kitchenette.

I plan to use this 8/3 AC as a multiwire branch circuit to feed a 120 volt 3000 watt water heater, the other side of this circuit will feed a 20 amp receptacle for a refrigerator.

This will mean I will have a single pole 35 and a single pole 20 feeding this multiwire branch circuit.

I see no problem with this, however my coworkers think I am nuts, and who would know that better then them.

Am I missing something, is this a NEC violation?

Any responses are appreciated.

Thanks, Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
2017 / 2014 NEC & Related Books and Study Guides
#89575 - 10/09/04 05:34 AM Re: Multiwire Branch Circuit with Unequal OCP
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Bob I think you comply with 210.4(C) and I assume that the common conductor of the circuit is insulated and that there is also an equipment grounding conductor. Where do I put the green sticker?
_________________________
George Little

Top
#89576 - 10/09/04 09:52 AM Re: Multiwire Branch Circuit with Unequal OCP
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
Go for it. Nothing says that the OCPD's have to be equal.
_________________________
John

Top
#89577 - 10/09/04 08:15 PM Re: Multiwire Branch Circuit with Unequal OCP
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
I know that this is picking nits, but if you use a #8 Cu for a 20A circuit, wouldn't you also be required to use #8 for the EGC? *grin* Of course, given your normal work situation, I'm guessing that this circuit is in pipe.

-Jon

Top
#89578 - 10/10/04 04:02 AM Re: Multiwire Branch Circuit with Unequal OCP
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
George, yes I have a white insulated grounded conductor.

electricman2 That is my thinking too.

Jon, I do not think you are nit picking, you are right on the money IMO.

If this was 8/3 MC cable the EGC would be 10 AWG which as you point out would be to small for the 20 amp circuit per 250.122(B)

This happens to be 8/3 AC cable, type AC cable does not have a copper EGC at all, it utilizes the armor as the EGC.

Thanks for the replies

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts