The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (ampherder), 184 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89574 - 10/09/04 03:13 AM Multiwire Branch Circuit with Unequal OCP
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I am currently remodeling office space, I have an existing 8/3 AC cable that runs from a panel 125' to a kitchenette.

I plan to use this 8/3 AC as a multiwire branch circuit to feed a 120 volt 3000 watt water heater, the other side of this circuit will feed a 20 amp receptacle for a refrigerator.

This will mean I will have a single pole 35 and a single pole 20 feeding this multiwire branch circuit.

I see no problem with this, however my coworkers think I am nuts, and who would know that better then them.

Am I missing something, is this a NEC violation?

Any responses are appreciated.

Thanks, Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
2014 / 2011 NEC & Related Books and Study Guides
#89575 - 10/09/04 05:34 AM Re: Multiwire Branch Circuit with Unequal OCP
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Bob I think you comply with 210.4(C) and I assume that the common conductor of the circuit is insulated and that there is also an equipment grounding conductor. Where do I put the green sticker?
_________________________
George Little

Top
#89576 - 10/09/04 09:52 AM Re: Multiwire Branch Circuit with Unequal OCP
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
Go for it. Nothing says that the OCPD's have to be equal.
_________________________
John

Top
#89577 - 10/09/04 08:15 PM Re: Multiwire Branch Circuit with Unequal OCP
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
I know that this is picking nits, but if you use a #8 Cu for a 20A circuit, wouldn't you also be required to use #8 for the EGC? *grin* Of course, given your normal work situation, I'm guessing that this circuit is in pipe.

-Jon

Top
#89578 - 10/10/04 04:02 AM Re: Multiwire Branch Circuit with Unequal OCP
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
George, yes I have a white insulated grounded conductor.

electricman2 That is my thinking too.

Jon, I do not think you are nit picking, you are right on the money IMO.

If this was 8/3 MC cable the EGC would be 10 AWG which as you point out would be to small for the 20 amp circuit per 250.122(B)

This happens to be 8/3 AC cable, type AC cable does not have a copper EGC at all, it utilizes the armor as the EGC.

Thanks for the replies

Bob