We installed security lighting on a number of storage shed buildings. These are buildings consisting of individual storage areas (ex: 8 per building) The lighting circuit is taken from a main building underground and comes up at each building with the light fixture controlled by a photo cell. There is no wiring inside of the storage sheds except for one that has a receptacle. The local inspector wants two ground rods installed at each building. I cannot find any requirement for this in the code and I'm wondering if any of you out there can shed (no pun intended)a little light on this situation. I feel no ground rods would be required since there is only one circuit and none of the wiring is installed inside of the sheds.
Thanks in advance
Ron
Top
2017 / 2014 NEC & Related Books and Study Guides
#89567 - 10/07/04 07:54 PM Re: Ground rods at each building
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
The rule is 250.32(A), but it sounds like you meet the exception. If you need two circuits, use a multiwire branch circuit and call it one circuit, as discussed in 210.4
_________________________
Ryan Jackson,
Salt Lake City
Top
#89568 - 10/07/04 09:07 PM Re: Ground rods at each building
Norstarr Offline
Member
Registered: 09/25/04
Posts: 86
Loc: Wi
Thank you, Ryan. Your info was of great help. Not sure what you mean by using a multiwire branch circuit and call it one circuit. To me a multiwire branch circuit is two or more circuits which would require the ground rods at each building in which I would install the multiwire branch circuit.
Thanks again
Ron
Top
#89569 - 10/07/04 09:49 PM Re: Ground rods at each building
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Quote:
Exception: A grounding electrode at separate buildings or structures shall not be required where only one branch circuit supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the conductive non–current-carrying parts of all equipment.
Sounds like you need a ground wire too, for that exception. But I see a multi-wire as one ciruit if they are a tied breaker, as well. Good luck, or it sounds like a a time to rent a 50lbs jack hammer, they drop rods fast!
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#89570 - 10/07/04 11:17 PM Re: Ground rods at each building
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
A multiwire branch circuit is considered a single circuit for this application. Read the last sentence in 225.30. Multi-pole breakers or handle ties on individual breakers are not required. If only one multiwire circuit supplies each building a grounding electrode is not required. A disconnect is required for each building (255.33).

Curt
_________________________
Curt Swartz
Top
#89571 - 10/08/04 06:33 AM Re: Ground rods at each building
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Take a look at 210.4, where is says that a multiwire is permitted to be considered multiple circuits. If that is permitted, than by using the english language, the contrary is true as well...a multiwire branch circuit can be considered one circuit.
_________________________
Ryan Jackson,
Salt Lake City
Top
#89572 - 10/09/04 09:07 AM Re: Ground rods at each building
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
If we look at the Article 100 definition of mutiwire branch circuit we see that it is defined as a circuit not circuits

Quote:
Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#89573 - 10/09/04 02:28 PM Re: Ground rods at each building
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
As Bob has noted, a multiwire branch circuit is just that 'a' branch circuit as per Art 100. There are other locations in the NEC that permit the use of a multiwire branch circuit as more than one circuit. Knowing these locations and how to understand them is a good benefit to understanding the NEC.
210.4 permits the use of a multiwire branch circuit as more than one - a good place we see this regularly is in kitchens for the small appliance branch circuits.

Pierre
_________________________
Pierre Belarge
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (Admin, sparkyinak), 74 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals