#89533 - 09/25/04 04:19 PM Busway feeding entire building
Active 1 Offline
Member
Registered: 02/22/03
Posts: 687
Loc: Grayslake IL, USA
I was at a small factory about 10,000 sf the other day and noticed something that did not look right to me.

There were 2 services because the bilding was devided in the past. Both 400 amp 3 phase. They each went into a 400 amp Disco and then straight to a bussway maybe 70' long. Off the 2 bussways fed the entire building. Maybe 6-8 panels in different locations 200 and 100 amp were run off the bussway. From those panels it must have fed the lighting, front office, HVAC, and general outlets. They also had the factory machines and a step up transformer off the same duct.

I looked in the NEC and could not find any violations with this. What's your opinion on this. Acceptibale or unaccepticable?

Tom
Top
2017 / 2014 NEC & Related Books and Study Guides
#89534 - 09/25/04 05:12 PM Re: Busway feeding entire building
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Regarding the bus duct, I can't think of anything wrong here. This is a very flexible means of distributing power, kind of expensive, but if the power requirements change on a regular basis, might end up being the least expensive way of doing things.
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#89535 - 09/27/04 03:03 AM Re: Busway feeding entire building
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
This is a common way of feeding high rise office buildings. Come out of the service gear with 4000A bus duct and run it vertical through the electric rooms. Each room has a place to set a couple of disconnects on the bus to feed the floor. From what you describe I see nothing wrong.
Top
#89536 - 09/27/04 02:22 PM Re: Busway feeding entire building
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
so, how much DOES a bus weigh?
Top
#89537 - 09/27/04 02:26 PM Re: Busway feeding entire building
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
A lot when you are on the other end of the rope hauling them up the elevator shaft.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 101 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals