The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 196 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 4 1 2 3 4 >
Topic Options
Rate This Topic
#89386 - 09/13/04 06:08 PM Romex in commercial buildings?
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Alright, I'm posting this to stir everybody up! (Kidding ) And, I'm not trying to put anyone down, or criticize the many varied methods that are allowed in various places. (Although, it is not allowed in many places, some places it is.)

But would you:
Use romex in a church?
Use romex in a grocery store?
Use romex in a 40 story office bulding?
Use romex for a 277/480v circuit?

My answer is No, to all of the above.
Even if you could, would you?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
2014 / 2011 NEC & Related Books and Study Guides
#89387 - 09/13/04 06:29 PM Re: Romex in commercial buildings?
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Yes, why not? I don't see the problem.

I have seen NM cable used in 3 of the 4 applications you mentioned (except the 40 story building) without any problems.

I've never understood the resistance to using NM.

It is a safe, code compliant wiring method and is very cost effective.

I don't buy the "smoke toxicity" argument often cited as a reason for disallowing NM cable in commercial spaces. What about the other toxic smoke that is contributed when carpet, computers, office furniture, paint, and other chemical compounds burn?

Peter
_________________________
Peter

Top
#89388 - 09/14/04 02:05 AM Re: Romex in commercial buildings?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I think it looks out of place in many of the locations you list. But without some facts to show it is unsafe what is the problem.

I have some experience with the grocery store question and when there is a reason we have to run MC in place of NM the office tells us it is about a $60,000 change. (80,000 to 100,000 sq ft stores) So if you try to bid the job MC when everyone else is bidding NM there is not much chance you will get the job.

We service about 100 large grocery stores and most are NM, very few service calls have to do with the NM. Most calls are failures of THWN in under slab raceways or problems with breakers and relays.

Hey stir things up.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89389 - 09/14/04 02:39 AM Re: Romex in commercial buildings?
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
334.12(A)(1)of the 2002 NEC does't allow romex as open runs above drop ceilings in other than one & two family and multifamily dwellings.

Article 518 does't allow romex in portions of that building that are designed for assembly of more than 100 persons.This section could apply all of the areas you mentioned.

shortcircuit

Top
#89390 - 09/14/04 03:08 AM Re: Romex in commercial buildings?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
518 has no influence on a grocery store or a 40 story building as a whole.

518 will keep NM out of the church assembly area it does not keep it out of the ancillary areas like bathrooms, offices, hallways, etc.

Yes 334.12(A)(1) has changed the rules for most, but being a MA resident that was amended so it is not a consideration for me.

 Quote:
Use romex for a 277/480v circuit?


NM is rated 600 volt for a reason and yes we use it.

I will admit I am not comfortable pushing a 12/3 out of the way with 480 volt, 3 phase live in it.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89391 - 09/14/04 12:36 PM Re: Romex in commercial buildings?
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Bob,

 Quote:
But without some facts to show it is unsafe what is the problem.


I agree. I wanted to bring this one up because MA did cite a very safe history of NM use, hence the suspended ceiling ammendment in the MEC. I'm pretty sure I read that in the ROPs, but I can't quite remember.

Correct me if I am wrong, but didn't the MEC also allow NM to be used in buildings of any height long before the '02 NEC made the change?

Since I am not from MA I am going by hearsay and may be totally screwing this one up.

 Quote:
I will admit I am not comfortable pushing a 12/3 out of the way with 480 volt, 3 phase live in it.


I don't think anyone would be. Nobody should feel comfortable pushing any live cable around, MC, AC or otherwise.

Peter
_________________________
Peter

Top
#89392 - 09/14/04 07:09 PM Re: Romex in commercial buildings?
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Alright here we go.... There reason I brought this up is I had an arguement with a PM about it a while back. And everytime I see NM in a situation that I "feel uncomfortable" with it, I don't think anyone else should be either. Hense, I won't put it in! If I, not a layman, am not comfortable with it as a proffessional, why should I expect to the layman to be. It's a little too much philosophy isn't it?

So, this PM (when the code changes were coming) out said, "Yeah, you can now use NM anywhere! You can use romex in a church, a grocery store, a 40 story office bulding?"

I said, "Well when it comes down to it, NO I WON'T!" Then sited the quote at the bottom of the post.

The Code is a minimum standard, right? Wouldn't want you doctor to do the bare minimum, right?

We don't use it in Theaters, and places of assembely do to toxic possiblities in a fire, and rapid fire spread. What makes a church any different than the use of a theater? A grocery store may as well be a place of assembly, on average 100 to 300 people could be "assembed" in one building at any given time. Imagine Sept 11, if those buildings were done in NM? Quite a few people assembled there. Extreme example, but still fewer people would have made it out if it had been wired in NM.

Bob, you said, "I will admit I am not comfortable pushing a 12/3 out of the way with 480 volt, 3 phase live in it." Neither am I! One reason I won't install it, for that voltage, rated for it or not. But that's me. I don't think it provides the physical protection of MC, or AC.

Like I said, in the original post. I'm not trying to put anyone down, or criticize... I am just sick of people expecting the bare minimum from me! If I miss a bid because I went MC, against a guy doing it with NM, my wallets empty, but my conscience is clean.

Fortunatley, I don't have deal with it yet, as SF doesn't allow NM in commercial buildings due the higher fire rating imposed on them, than on residential. So when I do have to worry about it, someone is going to have to show me the Fire Rating of the building before I decide to use NM, or not.

 Quote:
Commentary from 334.10 A well-established means of codifying fire protection and fire safety requirements is to classify buildings by types of construction, based on materials used for the structural elements and the degree of fire resistance afforded by each element. The five fundamental construction types used by the model building codes are Type I (fire resistive), Type II (noncombustible), Type III (combination of combustible and noncombustible), Type IV (heavy timber), and Type V (wood frame). Types I and II basically require all structural elements to be noncombustible, whereas Types III, IV, and V allow some or all of the structural elements to be combustible (wood).
The selection of building construction types is regulated by the building code, based on the occupancy, height, and area of the building. The local code official or the architect for a building project can be consulted to determine the minimum allowable (permitted) construction type for the building under consideration. When a building of a selected height (in feet or stories above grade) and area is permitted to be built of combustible construction (i.e., Types III, IV, or V), the installation of nonmetallic sheathed cable is permitted. The common areas (corridors) and incidental and subordinate uses (laundry rooms, lounge rooms, etc.) that serve a multifamily dwelling occupancy are also considered part of the multifamily occupancy, thereby allowing the use of nonmetallic sheathed cable in those areas.
If a building is to be of noncombustible construction (i.e., Type I or II) by the owner's choice, even though the building code would permit combustible construction, the building is allowed to be wired with nonmetallic sheathed cable. In such an instance, nonmetallic sheathed cable may be installed in the noncombustible building because the Code would have permitted the building to be of combustible construction.
Annex E provides charts and other explanatory information to assist the user in understanding and categorizing the exact types of construction under consideration. A table to cross reference building types to the various building code types of construction is provided in Annex E also.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#89393 - 09/14/04 07:36 PM Re: Romex in commercial buildings?
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
e57,

 Quote:
Imagine Sept 11, if those buildings were done in NM? Quite a few people assembled there. Extreme example, but still fewer people would have made it out if it had been wired in NM.


Huh? That is a ridiculous statement to make. Do you have any facts to back this up? How on earth does the wiring method factor into that??

Until hard facts prove otherwise, I maintain that NM is a safe, code compliant and cost effective way to do the job.

I'm sure I am biased because the use of NM has widespread acceptance where I live. But I still don't understand where this dislike, almost hatred, of NM comes from at all.

Peter
_________________________
Peter

Top
#89394 - 09/14/04 08:10 PM Re: Romex in commercial buildings?
macmikeman Offline
Member

Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
Ok here we go.. If it is a multi use commercial situation such as a strip mall, and you use romex to wire lets say a furniture store or shoe store, but nearby they put in a greasy spoon fast food counter, you could get some serious rat chew the romex up problems over time. I have seen just such a situation before firsthand. The application was a single story strip mall made with timber and had drop ceilings. the rats were able to get around the firewalls (mostly where trades did a lousy job of sealing). I found sections of very nicely completly stripped energized cable runing in metal studs behind sheetrock which was removed for remodel work. At least the guy who ran it used insulated bushings where he passed thru stud openings.

Top
#89395 - 09/14/04 11:51 PM Re: Romex in commercial buildings?
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Ok Peter,
Yeah, the 911 referance was a bit over the top... But smoke and fire travel facts are well documented. You can try it yourself. Put a 3' length of MC and NM on a brick wall, hit them both with a MAPP gas torch at the bottom, judge for yourself.

And, it's not that I hate it. But like anything else, it has a place. Single family home under 3 stories, fine! 6 story apt. building, no. A 40 story building NO WAY!
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason