The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 11:04 PM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 6
renosteinke 6
Potseal 4
Who's Online
0 registered (), 274 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89326 - 09/09/04 07:32 PM GEC
mustangelectric Offline

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Is there ever a time where a MAIN PANELBOARD for a Sinfgle Fam Dwelling would NOT have a #4 bare ground for cold water ground? copper piping.

here in Arkansas the GEC goes from the Ground rod to the METER BASE. In Kentucky it is from the Panelboard to the Ground Rod. If there is a copper water line, you need a COLD WATER BOND..usually a #6 for 100A and #4 for 200A this ALWAYS goes to the MAIN PANELBOARD..

i saw a house today that only had a gec from the main disc at the other ground in the panel..

this looked wrong to me..

the feed was a 4 conductor SER type cable..

thanks for any replies..

Electricity has no respect for ignorance!

2014 / 2011 NEC & Related Books and Study Guides
#89327 - 09/09/04 07:51 PM Re: GEC
Dave55 Offline

Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
Allways check with the AHJ.


#89328 - 09/09/04 08:15 PM Re: GEC
Ryan_J Offline

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
GEC's are required to go from the electrode to the service equipment. If the disco at the meter is the service equipment, and it sounds like it is, this is code compliant.
Ryan Jackson,
Salt Lake City

#89329 - 09/09/04 09:21 PM Re: GEC
gfretwell Offline


Registered: 07/20/04
Posts: 9025
Loc: Estero,Fl,usa
It can be anywhere from the load end of the drop to the disconnect enclosure.

250.24 Grounding Service-Supplied Alternating-Current Systems.
(A)(1) General. The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.
Greg Fretwell

#89330 - 09/10/04 08:34 PM Re: GEC
harold endean Offline

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
What if all of the water piping in the house is PLASTIC? What do you ground to?