The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
10/24/16 06:25 AM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (mbhydro), 315 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89303 - 09/08/04 06:49 PM PVC Conduit Under Deck
mustangelectric Offline

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
If there is a raised deck that will be the foundation/pedastal for a hot tub/spa, would a PVC conduit supplying the unit from below the deck need to be buried to any specific depth or would it even matter? I do not see any benifit to burying the conduit since it will have a deck built over it.

thanks for any replies.

Electricity has no respect for ignorance!

2014 / 2011 NEC & Related Books and Study Guides
#89304 - 09/08/04 07:09 PM Re: PVC Conduit Under Deck
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
You do not have to bury it, but you will then have to secure it.

If this is small PVC 1/2", 3/4" or 1" you will need to secure it every 3'.

Bob Badger
Construction & Maintenance Electrician