#89292 - 09/08/04 06:27 PM EGC
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
What size Equipment Grounding Conductor would be installed with the tap conductors to a 200a switch. The feeder overcurrent protection is 600 a and the tap conductors run 25 feet and are 3/0 copper and terminate in a 200 ampere switch with 200 a fuses installed.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#89293 - 09/08/04 06:42 PM Re: EGC
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
The EGCs run with the tap conductors will need to be 1/0 copper. You must base the EGC on the overcurrent device it would have be able to open. In this case that would be the 600 amp feeder.

Once you leave the 200 amp switch the EGC may be 6 awg copper.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#89294 - 09/09/04 04:09 AM Re: EGC
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
I agree with you iwire, but it's not thst clear in the NEC. It's one of those things left silent and you need to use logic to figure it out, like you put it, what overcurrent device will it be opening.
_________________________
George Little
Top
#89295 - 09/09/04 05:14 AM Re: EGC
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
As usual the handbook does a better job of explaining things. This is commentary from 250.122
"Equipment grounding conductors on the load side of the service disconnecting means and overcurrent devices are sized based on the size of the feeder or branch circuit overcurrent devices ahead of them."
_________________________
Greg Fretwell
Top
#89296 - 09/09/04 06:33 AM Re: EGC
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
When in doubt, check out 250.4(A)(5).
_________________________
Ryan Jackson,
Salt Lake City
Top
#89297 - 09/09/04 09:45 AM Re: EGC
electricman2 Offline
Member
Registered: 11/09/03
Posts: 269
Loc: Thomasville, NC USA
In table 250.122 the heading states "Rating or Setting of Automatic Overcurrent Device in Circuit Ahead of Equipment, conduit, etc. Sometimes it takes careful reading to get the intent.

[This message has been edited by electricman2 (edited 09-09-2004).]
_________________________
John
Top
#89298 - 09/09/04 02:24 PM Re: EGC
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
electricman2 That is exactly what I would have pointed to.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#89299 - 09/09/04 02:37 PM Re: EGC
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
Bob, where did the 1/0 come from? Table 250.66? or 250.122?
_________________________
Peter
Top
#89300 - 09/09/04 02:44 PM Re: EGC
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Table 250.122 and it is worth mentioning that the EGCs never have to be larger than the associated circuit conductors. 250.122(A)

[This message has been edited by iwire (edited 09-09-2004).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#89301 - 09/09/04 06:10 PM Re: EGC
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
Bob,

In that case, wouldn't #1 CU be sufficient for a 600 amp OCPD by table 250.122?

Just trying to figure this out as I rarely work on stuff that large.

Peter
_________________________
Peter
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals