The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 21
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
2 registered (Admin, dougwells), 76 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#89292 - 09/08/04 06:27 PM EGC
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
What size Equipment Grounding Conductor would be installed with the tap conductors to a 200a switch. The feeder overcurrent protection is 600 a and the tap conductors run 25 feet and are 3/0 copper and terminate in a 200 ampere switch with 200 a fuses installed.
_________________________
George Little

Top
2017 / 2014 NEC & Related Books and Study Guides
#89293 - 09/08/04 06:42 PM Re: EGC
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
The EGCs run with the tap conductors will need to be 1/0 copper. You must base the EGC on the overcurrent device it would have be able to open. In this case that would be the 600 amp feeder.

Once you leave the 200 amp switch the EGC may be 6 awg copper.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89294 - 09/09/04 04:09 AM Re: EGC
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I agree with you iwire, but it's not thst clear in the NEC. It's one of those things left silent and you need to use logic to figure it out, like you put it, what overcurrent device will it be opening.
_________________________
George Little

Top
#89295 - 09/09/04 05:14 AM Re: EGC
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
As usual the handbook does a better job of explaining things. This is commentary from 250.122
"Equipment grounding conductors on the load side of the service disconnecting means and overcurrent devices are sized based on the size of the feeder or branch circuit overcurrent devices ahead of them."
_________________________
Greg Fretwell

Top
#89296 - 09/09/04 06:33 AM Re: EGC
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
When in doubt, check out 250.4(A)(5).
_________________________
Ryan Jackson,
Salt Lake City

Top
#89297 - 09/09/04 09:45 AM Re: EGC
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
In table 250.122 the heading states "Rating or Setting of Automatic Overcurrent Device in Circuit Ahead of Equipment, conduit, etc. Sometimes it takes careful reading to get the intent.

[This message has been edited by electricman2 (edited 09-09-2004).]
_________________________
John

Top
#89298 - 09/09/04 02:24 PM Re: EGC
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
electricman2 That is exactly what I would have pointed to.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89299 - 09/09/04 02:37 PM Re: EGC
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Bob, where did the 1/0 come from? Table 250.66? or 250.122?
_________________________
Peter

Top
#89300 - 09/09/04 02:44 PM Re: EGC
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Table 250.122 and it is worth mentioning that the EGCs never have to be larger than the associated circuit conductors. 250.122(A)

[This message has been edited by iwire (edited 09-09-2004).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89301 - 09/09/04 06:10 PM Re: EGC
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Bob,

In that case, wouldn't #1 CU be sufficient for a 600 amp OCPD by table 250.122?

Just trying to figure this out as I rarely work on stuff that large.

Peter