#89125 - 09/03/04 01:07 PM Cables in suspended ceiling
Bill39 Offline
Member
Registered: 11/28/01
Posts: 75
Loc: Indianapolis, IN, USA
I'd like some opinions on if this type installation would meet the NEC:

Short version: When can shielded cables be ran in a suspended ceiling and not be in a raceway? Two types of cables, one with 120VDC for small motors and other is 24VDC for sensors, & encoders.

Long version:
Have a large custom control panel (120VAC max) and some test stands w/small DC motors, encoders, and sensors. All are in a lab/testing room. We need to run shielded cables between the control panel and test stands. Conduits (1 for low voltage & 1 for 120VDC) will extend up into a suspended ceiling and end. In the ceiling the cables are to be supported by the metal joists, and ty-rapped together.
Top
2017 / 2014 NEC & Related Books and Study Guides
#89126 - 09/03/04 01:34 PM Re: Cables in suspended ceiling
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Two questions spring to mind, is this a fire rated ceiling and is this a plenum for return air?
_________________________
Greg Fretwell
Top
#89127 - 09/03/04 01:38 PM Re: Cables in suspended ceiling
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Are these cables a chapter 3 wiring method?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#89128 - 09/04/04 09:20 AM Re: Cables in suspended ceiling
hbiss Offline
Member
Registered: 12/16/03
Posts: 886
Loc: Hawthorne, NY USA
Not so much as would they need to be run in a raceway but what is the required wiring method. I doubt any would have to be run in raceway if the correct wiring is used.

Even with raceway you will have to determine whether these circuits are CL1, 2 or 3 and proceed from there. If any are CL1 you may not be able to use the wire you have even with raceway.

-Hal
_________________________
www.myphonetechs.com
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 14 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals