The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 201 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#8910 - 04/09/02 04:33 AM M-I-C-K-E-Y-M-O-U-S-E
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Do you make your (larger) terminations straight into the lugs, or make large loops (Mickey Mouse Ears)?
Why?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#8911 - 04/09/02 02:08 PM Re: M-I-C-K-E-Y-M-O-U-S-E
DLinton Offline
Member

Registered: 03/19/02
Posts: 19
Loc: Holcomb, KS. USA
I use the loop (mickey mouse ears) mainly for two reasons. One, larger conductors are harder to get bent around and go into a lug straight on after cutting to length, if they are to go straight in from opening to lug. Second, larger conductors in my opinion ( if not properly torqued) tend to become loose at the lug easier than smaller conductors and with loops there might be a chance to save wire, time and of course cost, when you need to cut back on the conductor after it became damaged from the heat at the lug.
Just my idea.
Dan

Top
#8912 - 04/09/02 04:46 PM Re: M-I-C-K-E-Y-M-O-U-S-E
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
There's been some interesting chat about this , drifting off into the EE land, loops vs. an S ...if I remember the S's fared better, so I've been an S man since.

Top
#8913 - 04/09/02 06:13 PM Re: M-I-C-K-E-Y-M-O-U-S-E
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
How about bending radii? Is a loop more acceptable than an S?

Top
#8914 - 04/09/02 08:34 PM Re: M-I-C-K-E-Y-M-O-U-S-E
The Watt Doctor Offline
Member

Registered: 12/23/01
Posts: 443
Loc: Mont Belvieu, TX
My wife goes to Disney World at least once a year. I try to stay out of that place. As for electrical work, I try to stay away from anything that's "Mickey Mouse", and that includes Old Mickey's ears. Let's face it. Anything with ears that big is going to give you trouble. Think about it, ear infections, ear mites, wax build up, etc, etc, etc.
So, The Watt Doctor's perscription for problems with mouse ears is "Decon", but if you have problems with terminations notice the following:
1. Form the wire in the space provided (panel, switchgear, disconnect, etc) in neat and workman like manner.
2. Torque mechanical lugs to manufacturer's specs.
3. Don't use mechanical lugs. Go buy the crimp on (compression) type.
I hope that all who read this realize that it's just my opinion, and if you have a method that works, don't stop on my account. I would, on larger wire, begin to question the bending radius of the wire. I would also begin to wonder about the effects of those types of bends in a fault situation.

Zoological Regards,
Doc
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX

Top
#8915 - 04/11/02 12:25 PM Re: M-I-C-K-E-Y-M-O-U-S-E
gpowellpec Offline
Member

Registered: 12/06/00
Posts: 128
Loc: Irving, Tx USA
Okay, Watt Doctor.
You opened the door for discussion of "the effects of those types of bends in a fault situation" so lets hear your prognosis. This was a controversial thread on another forum.

Top
#8916 - 04/13/02 10:47 PM Re: M-I-C-K-E-Y-M-O-U-S-E
The Watt Doctor Offline
Member

Registered: 12/23/01
Posts: 443
Loc: Mont Belvieu, TX
Mr. Powell,
I'm sure that it will, or would, raise as much of a fuss on this forum as it did on the other. Therefore, I respectfully request that you post a link to the other thead, and after I read it, I may very well flame myself.

Respectfully,
Doc
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX

Top
#8917 - 04/17/02 01:39 PM Re: M-I-C-K-E-Y-M-O-U-S-E
gpowellpec Offline
Member

Registered: 12/06/00
Posts: 128
Loc: Irving, Tx USA
Doc,
I don't remember exactly where and when the discussion was. Think it was on IAEI the middle of last year. I haven't been to that site in a good while. Think they changed format and required new registration so I dropped out. Since no injuries or deaths have been attributed to mickey mouse ears a discussion may not be worth the emotional turmoil.

Top
#8918 - 04/17/02 02:52 PM Re: M-I-C-K-E-Y-M-O-U-S-E
The Watt Doctor Offline
Member

Registered: 12/23/01
Posts: 443
Loc: Mont Belvieu, TX
Emotional turmoil ....."Roger that, Mr. Powell"
I will say, that I read, and post on this forum first, and foremost to have fun. Second, and third reasons, in no particular order, to learn, and as some people in my neck of the woods might say, "To learn others."
I will submit, or admit that my responce to your "open door" post was, in all truth, a "cop out". The fact is, I don't like to argue on these forums (though I have been known to vent from time to time).
Instead of making vague references to bending radius, and fault current, I should have said, "Hey guys, I just don't like it. To me, it doesn't look good." I must say, "I think my "vague references" can be argued."
You're a gentleman, Mr. Powell, and best regards to you and yours.

Keeping the door open, so to speak,
Doc