#89072 - 08/27/04 08:26 PM ENT is it plenum rated.
master44 Offline
Member
Registered: 12/01/02
Posts: 13
Loc: Clay Center, Kansas USA
I am wiring an office that has a suspended ceiling that serves as a return air space above it. Code book says I can use ent above suspended ceilings if it is fire rated at 15 minutes. It doesn't say I can't use it either in this situation. In the Nec it does say that ent is flame retardent. Can I use it? What is your opinion.
Top
2017 / 2014 NEC & Related Books and Study Guides
#89073 - 08/27/04 08:27 PM Re: ENT is it plenum rated.
hbiss Offline
Member
Registered: 12/16/03
Posts: 886
Loc: Hawthorne, NY USA
No.

-Hal
_________________________
www.myphonetechs.com
Top
#89074 - 08/28/04 07:16 AM Re: ENT is it plenum rated.
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
300-21(c)1.no ENT
Top
#89075 - 08/28/04 07:19 PM Re: ENT is it plenum rated.
master44 Offline
Member
Registered: 12/01/02
Posts: 13
Loc: Clay Center, Kansas USA
Thanks guys, I missed that in the code book.
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals