The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 139 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#89038 - 08/26/04 12:02 PM BX in a MEDICAL Facility
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Is BX or MC cable allowed in a rural medical clinic with patient exam rooms and xray? wood structure single story

If I remeber correctly it is NOT.

thanks for any reply
_________________________
Electricity has no respect for ignorance!

Top
2014 / 2011 NEC & Related Books and Study Guides
#89039 - 08/26/04 02:52 PM Re: BX in a MEDICAL Facility
trekkie76 Offline
Member

Registered: 06/19/04
Posts: 219
Loc: baileyville, maine, usa
517-2 def. of a health care facilities.it includes a clinic. 517-13(a) lists MC as an acceptable wiring method, as long as it's outer metal sheath is identified as a grounding path. the MC cable has to have an insulated ground in it. It is usually called Hospital grade, and has a green paint on it.

[This message has been edited by trekkie76 (edited 08-26-2004).]

Top
#89040 - 08/26/04 04:05 PM Re: BX in a MEDICAL Facility
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Very unlikely you will get MC with a sheath that is an acceptable grounding conductor, I use MC all the time and have never seen the type of MC that has the right kind of armor for grounding.

What you need is hospital grade AC cable.

The outer armor is a listed grounding conductor along with the added green grounding conductor.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89041 - 08/27/04 04:23 AM Re: BX in a MEDICAL Facility
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Would there be any difference between hospital grade AC and hospital grade MC...other than the 'red hat' requirement

-Jon

Top
#89042 - 08/27/04 06:05 AM Re: BX in a MEDICAL Facility
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Jon, there is no such thing as HG MC.

Also remember that HCFC can not be used for Emergency Branch wiring.

Roger

Top
#89043 - 08/27/04 07:47 AM Re: BX in a MEDICAL Facility
capt al Offline
Member

Registered: 06/20/04
Posts: 203
Loc: Norton, Ma USA
Jon look at 250.118 (9) and 250.118 (11). That will explain the difference between AC & MC. Hospital grade Mc I'm told is custom order. Probably explains why I and iwire have not seen it.

Top
#89044 - 08/27/04 09:26 AM Re: BX in a MEDICAL Facility
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Capt al, once again there is no such thing as hospital grade MC. There is MC with a sheath that is recognized as a ground per 250.118, and it is allowed for redundant grounding per 517.13, but that is not a Health Care Facility Cable.

Type HCFC is a true Armored Cable.

Go here for more info

Roger



[This message has been edited by Roger (edited 08-27-2004).]

Top
#89045 - 08/27/04 01:39 PM Re: BX in a MEDICAL Facility
trekkie76 Offline
Member

Registered: 06/19/04
Posts: 219
Loc: baileyville, maine, usa
well then, someone should start making Hospital grade MC becuase it is listed as a wiring method in 517-13a. Just because you have never seen it doesn't mean it can't be used or doesn't exist.

Top
#89046 - 08/27/04 03:33 PM Re: BX in a MEDICAL Facility
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Trekkie, did you check the link I posted?

As far as MC meeting the requirements of 517-13 (99 NEC reference) some types can meet this requirement and the smooth type is one of these, but this still is not a "Hospital Grade" cable.

Yes, I have seen the smooth type MC, and you have too most likely. Some appliances have it installed from the factory, but as Iwire says it is not common in our field.

And I will say again, Hospital Grade MC does not exist, HCFC is an AC hybrid.

Roger

Top
#89047 - 08/27/04 04:45 PM Re: BX in a MEDICAL Facility
trekkie76 Offline
Member

Registered: 06/19/04
Posts: 219
Loc: baileyville, maine, usa
the original post asked if mc was acceptable as a wiring method in a hospital. it is

Top