The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 284 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89019 - 08/22/04 03:50 AM pool bonding
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Can you guys recommend a method to check an exsisting inground swimming pools bonding connections where they can't be seen...to a metal ladder or a diving board for exsample.Would a simple continuity test between the exposed #8 at the motor and the ladder be sufficient?

Top
2014 / 2011 NEC & Related Books and Study Guides
#89020 - 08/22/04 08:27 AM Re: pool bonding
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
You are going to need something very accurate in the sub ohm range to tell you much. I'm not sure what the resistance would be if you just had a ladder cup stuck in wet concrete but I bet it is a fairly low number.
I have an Ecos tester that might work. It can prove less than 1 ohm under a load.