The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 82 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89016 - 08/21/04 02:30 PM pool wiring methods
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
1.In a one family dwelling with a permanently installed pool, 680.21(A)(4) allows the use of nonmetallic sheathed cable in the interior of that dwelling or the interior of an accessory building as a wiring method for branch circuits to a pool motor. Yes or No?
2.If the pool motor is "hard wired" from the disconnect switch that is required by 680.21 and not cord and plug connected, then GFCI protection of that motor is not required. Yes or No?
3.Also 680.23 does'nt allow the use of nonmetalic sheathed cable as a wiring method in any case as the branch circuit supply on the line side feeding j-boxes and low voltage transformers listed for connection to the conduit that extends to the forming shell. Yes or No?

Top
2014 / 2011 NEC & Related Books and Study Guides
#89017 - 08/21/04 08:07 PM Re: pool wiring methods
dansan Offline
Junior Member

Registered: 08/05/04
Posts: 5
Loc: Murfreesboro TN USA
My opinion

1. yes , 680.21(a)(4) allows this only on 1 family dwellings

2. No, gfci protection is not required unless it is cord and plug connected 680.22(a)(5)

3. No, NM cable is not listed for use in a wet location and it must be a minimum #12 insulated equipment grounding conductor 680.23(F)(2)

Top
#89018 - 08/22/04 08:36 PM Re: pool wiring methods
Speedy Petey Offline
Member

Registered: 08/29/03
Posts: 175
Loc: Upstate, NY
Agree with Dan.
I don't see much controversy in any of these three questions. They are very clear areas of 680 IMO.