The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 202 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#88897 - 08/11/04 03:46 PM type "IC" recessed cans
ccdave Offline
Member

Registered: 01/27/03
Posts: 61
Loc: culver city,calif. usa
California inspectors and contractors:
what is your call on "IC" cans in the building envelope that requires insulation,
ie; older house without insulation installs 2 cans in the kitchen. any other ref. besides t-24 150(k)4?-thanks--dave

Top
2014 / 2011 NEC & Related Books and Study Guides
#88898 - 08/11/04 05:52 PM Re: type "IC" recessed cans
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
On the Contractor side:

From the get go, plan to use IC on any top floor, or unit seperation. (Condos or Apartments that might become condo's, odds are some has some secret plan to do just that.) Irreguardless of insulation or not. (If there's not any now, there will be!)

On of my first questions walking a job is "Is there any insulation, and where? Is there any plan to have insulation anywhere else? Are you sure?"

Some places will accept Non-IC boxed out from insulation, to eliminate contact with the insulation. 3-6" But its a call to your inspector...

Fire rating is diffrent ball of wax... But wise to note as well in the same topic.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#88899 - 08/20/04 07:25 PM Re: type "IC" recessed cans
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Here in NJ the building insp. are requiring IC cans in any area that doesn't have a floor above it. This way you can insulate up to the can and not loose heat through the can.

Harold