The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by Trumpy
Today at 05:25 AM
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
ESA Arc flash course
by frank
Yesterday at 04:25 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
0 registered (), 0 Guests and 172 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#88872 - 08/03/04 05:30 AM outdoor panel - to nipple or not to nipple
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Is it permissable to knock out a 2" hole near the top side of a outdoor panel?Plans are to knock out a 2" hole about 4" down from top on the left hand side and also knock a hole in the meter can to match so they will be even(appearance)Co-worker says no but we can`t find in nec.And also can I use pvc nipple or would it have to be water tight hub?

Top
2017 / 2014 NEC & Related Books and Study Guides
#88873 - 08/03/04 01:47 PM Re: outdoor panel - to nipple or not to nipple
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
There is a product on the market refered to as a "myers hub" or possibly a sealing type locknut

check this site out also http://www.electrician.com/articles/myers.htm
http://www.electricaldeals.com/html/search.php3?column=AllenNum&search=MYER&source=ovr this site has an illistration of a hub

If you install two one on the meter and the other at the panel I don't see a proble interconnecting with PVC (two male adapters and a nipple to fit)

charlie P

312.2 Damp, Wet, or Hazardous (Classified) Locations.
(A) Damp and Wet Locations. In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6 mm (ΒΌ in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof.
Exception: Nonmetallic enclosures shall be permitted to be installed without the airspace on a concrete, masonry, tile, or similar surface.

Top
#88874 - 08/03/04 05:33 PM Re: outdoor panel - to nipple or not to nipple
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
If a field-cut KO in a NEMA-3R enclosure wall is partially or completely above the elevation of factory KOs, a hub is most often in order.

The other concern is preservation of wire-bending space.

Top
#88875 - 08/03/04 06:55 PM Re: outdoor panel - to nipple or not to nipple
necbuff Offline
Member

Registered: 07/08/04
Posts: 27
Loc: Lebanon Tn USA
You can also use a sealing locknut and do what you are talking about doing.