The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 202 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#88831 - 08/02/04 06:10 PM cooktops
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
We set up a residential kitchen for an electric cooktop by running a 8-3 romex to the kitchen.The owner got a "Melie" cooktop which is 3 seperate units each rated at 2.8 KW ...mounted side by side only 30inches wide each with its own seperate flex wipp with 12 gauge wire in the flex. Can all 3 be connected to the 8-3 romex that we installed and protect them with a 40 amp breaker???

Top
2014 / 2011 NEC & Related Books and Study Guides
#88832 - 08/03/04 10:26 AM Re: cooktops
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
Yes. See 210.19(A)(3)exception 1.
_________________________
John

Top
#88833 - 08/03/04 05:49 PM Re: cooktops
shortcircuit Offline
Member

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Thanx electricman2!!!