The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/22/16 09:52 PM
International Wire Colour Codes
by Texas_Ranger
10/22/16 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 212 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#88831 - 08/02/04 06:10 PM cooktops
shortcircuit Offline

Registered: 06/27/04
Posts: 608
Loc: massachusetts
We set up a residential kitchen for an electric cooktop by running a 8-3 romex to the kitchen.The owner got a "Melie" cooktop which is 3 seperate units each rated at 2.8 KW ...mounted side by side only 30inches wide each with its own seperate flex wipp with 12 gauge wire in the flex. Can all 3 be connected to the 8-3 romex that we installed and protect them with a 40 amp breaker???

2014 / 2011 NEC & Related Books and Study Guides
#88832 - 08/03/04 10:26 AM Re: cooktops
electricman2 Offline

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
Yes. See 210.19(A)(3)exception 1.

#88833 - 08/03/04 05:49 PM Re: cooktops
shortcircuit Offline

Registered: 06/27/04
Posts: 608
Loc: massachusetts
Thanx electricman2!!!