#88813 - 07/30/04 10:48 AM to code or not to code that is the question
RandyO Offline
Member
Registered: 09/26/02
Posts: 28
OK we all know that an extenson cord made from SO and terminated into a jbox is not to code, but what if the jbox is permanently mounted.??? Would I get away with that. ???

[This message has been edited by RandyO (edited 07-30-2004).]
Top
2017 / 2014 NEC & Related Books and Study Guides
#88814 - 07/30/04 02:29 PM Re: to code or not to code that is the question
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
If you do not violate 400.8 and can justify yourself through 400.7, you are allowed. Otherwise, it would not comply.
_________________________
Ryan Jackson,
Salt Lake City
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (sparkyinak), 108 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals