The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 298 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#88729 - 07/13/04 10:41 AM Outside diesel tank
ayrton Offline

Registered: 12/21/01
Posts: 205
Loc: Pa
I have a customer w/a outdoor diesel tank which has a pump. (purpose to fill trucks)
It is not a pump like a gas station. Just a big cylindrical tank with a pump motor.
Need to run 115 cir from adjacent building.
All conduit to be surface mounted on interior wall, through to outside and pump location. Question is is this a Class 1 Div 1 area? diesel is not a gas, but has a flashpoint of 160F to 180F. I am mounting a disconnect w/in eysight of the pump behind the tank (about 12') Does it have to be explosion proof? Are EYS seals required. Customer wants keyswitch to turn on pump when filling. Assume I need EYS fitting there too. (never done explosion proof before). Will conduit in building have to be rigid? Would like to run EMT in building out to disconnect than rigid to pump. Acceptable??
Do not see "diesel" mentioned in 500 section of NEC.
Called inspection agency and they said treat diesel same as gas.

2014 / 2011 NEC & Related Books and Study Guides
#88730 - 07/13/04 02:27 PM Re: Outside diesel tank
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I don't believe that a diesal fuel dispenser is a hazardous location that would require seals, threaded pipe etc.

Take a look at 514.3(A)

Few things are harder to put up with than the annoyance of a good example.

#88731 - 07/13/04 03:06 PM Re: Outside diesel tank
ayrton Offline

Registered: 12/21/01
Posts: 205
Loc: Pa
It seems to me a tank outside cannot be a Class I area.

#88732 - 07/13/04 05:25 PM Re: Outside diesel tank
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
Lots of outside areas are Class 1 locations. Some are even Class 1 Division 1.

#88733 - 07/14/04 01:35 PM Re: Outside diesel tank
ayrton Offline

Registered: 12/21/01
Posts: 205
Loc: Pa
I still cannot determine from 500 sec of NEC whether or not this falls under a classified area. Is it up to me to determine or an engineer?

#88734 - 07/14/04 01:42 PM Re: Outside diesel tank
ayrton Offline

Registered: 12/21/01
Posts: 205
Loc: Pa
Diesel has a flashpoint of 160 deg F to 180 deg F. According to International fire Code Flammable liquid is anything under 100 deg F. So that tells me it is not a "flammable liquid", so it doesnt fall into a classification in Sec 500- of the NEC

#88735 - 07/14/04 03:12 PM Re: Outside diesel tank
Ryan_J Offline

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Diesel fuel does not fall into article 500.

Not classified.
Ryan Jackson,
Salt Lake City

#88736 - 07/16/04 12:52 PM Re: Outside diesel tank
walrus Offline

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
Seal Tite would be what I have used many times on Diesel, Kero, or 2 oil. Unless gasoline is on the same island.

#88737 - 08/09/04 02:11 PM Re: Outside diesel tank
dgillespie Offline
Junior Member

Registered: 12/12/03
Posts: 1
Loc: New Braunfels, Tx USA
I have the same situation here, and this is what I on...

Diesel fuel is considered combustible, not flammable. Therefore, a diesel dispensing area is unclassified, and associated electrical equipment and wiring need not comply with the requirements of Chapter 5. But it's common to wire diesel fuel dispensers adjacent to gasoline dispensers. If conduit for the diesel dispenser passes through the Class I, Div. 1 or 2 areas around the gasoline dispenser, the wiring methods and sealing requirements in Art. 501 apply.
I found this at

Hopes this helps.