#88729 - 07/13/04 10:41 AM Outside diesel tank
ayrton Offline
Member
Registered: 12/21/01
Posts: 201
Loc: Pa
I have a customer w/a outdoor diesel tank which has a pump. (purpose to fill trucks)
It is not a pump like a gas station. Just a big cylindrical tank with a pump motor.
Need to run 115 cir from adjacent building.
All conduit to be surface mounted on interior wall, through to outside and pump location. Question is is this a Class 1 Div 1 area? diesel is not a gas, but has a flashpoint of 160F to 180F. I am mounting a disconnect w/in eysight of the pump behind the tank (about 12') Does it have to be explosion proof? Are EYS seals required. Customer wants keyswitch to turn on pump when filling. Assume I need EYS fitting there too. (never done explosion proof before). Will conduit in building have to be rigid? Would like to run EMT in building out to disconnect than rigid to pump. Acceptable??
Do not see "diesel" mentioned in 500 section of NEC.
Called inspection agency and they said treat diesel same as gas.
Top
2017 / 2014 NEC & Related Books and Study Guides
#88730 - 07/13/04 02:27 PM Re: Outside diesel tank
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
I don't believe that a diesal fuel dispenser is a hazardous location that would require seals, threaded pipe etc.

Take a look at 514.3(A)

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#88731 - 07/13/04 03:06 PM Re: Outside diesel tank
ayrton Offline
Member
Registered: 12/21/01
Posts: 201
Loc: Pa
It seems to me a tank outside cannot be a Class I area.
Top
#88732 - 07/13/04 05:25 PM Re: Outside diesel tank
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
ayrton,
Lots of outside areas are Class 1 locations. Some are even Class 1 Division 1.
Don
_________________________
Don(resqcapt19)
Top
#88733 - 07/14/04 01:35 PM Re: Outside diesel tank
ayrton Offline
Member
Registered: 12/21/01
Posts: 201
Loc: Pa
I still cannot determine from 500 sec of NEC whether or not this falls under a classified area. Is it up to me to determine or an engineer?
Top
#88734 - 07/14/04 01:42 PM Re: Outside diesel tank
ayrton Offline
Member
Registered: 12/21/01
Posts: 201
Loc: Pa
Diesel has a flashpoint of 160 deg F to 180 deg F. According to International fire Code Flammable liquid is anything under 100 deg F. So that tells me it is not a "flammable liquid", so it doesnt fall into a classification in Sec 500- of the NEC
Top
#88735 - 07/14/04 03:12 PM Re: Outside diesel tank
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Diesel fuel does not fall into article 500.

Not classified.
_________________________
Ryan Jackson,
Salt Lake City
Top
#88736 - 07/16/04 12:52 PM Re: Outside diesel tank
walrus Offline
Member
Registered: 07/25/02
Posts: 680
Loc: Bangor Me. USA
Seal Tite would be what I have used many times on Diesel, Kero, or 2 oil. Unless gasoline is on the same island.
Top
#88737 - 08/09/04 02:11 PM Re: Outside diesel tank
dgillespie Offline
Junior Member
Registered: 12/12/03
Posts: 1
Loc: New Braunfels, Tx USA
I have the same situation here, and this is what I found...read on...

Diesel fuel is considered combustible, not flammable. Therefore, a diesel dispensing area is unclassified, and associated electrical equipment and wiring need not comply with the requirements of Chapter 5. But it's common to wire diesel fuel dispensers adjacent to gasoline dispensers. If conduit for the diesel dispenser passes through the Class I, Div. 1 or 2 areas around the gasoline dispenser, the wiring methods and sealing requirements in Art. 501 apply.
I found this at http://ecmweb.com/conference/holt/electric_preventing_fires_gas/

Hopes this helps.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 20 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals