The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 192 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#88643 - 07/02/04 05:41 AM V.F.D. calcs
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
30 Hp with V.F.D.
430.6 & 430.150
30 hp =40amps at 460 volts
40x150%=60amps
wire size=3#6s &1#10
Disconnect Switch=60amp
Should disconnect switch be up sized to 100 amp (fuseable).Seems to be hitting it right on the mark? wondered if maybe to close??

75hp 460v 3 phase (96 amps)
96x150%=144 amps
wire size=3#1s&1#8
Disconnect switch =100amps

Hows it look guys don;t have into off name plates of VFD so using 430.6c

Top
2014 / 2011 NEC & Related Books and Study Guides
#88644 - 07/02/04 05:43 AM Re: V.F.D. calcs
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Opps Disconnect switch 150 amps not 100 amps

Top
#88645 - 07/02/04 06:41 AM Re: V.F.D. calcs
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Take a look at 430.2.

I do not see an option for using the tables as far as the VFD is concerned.

[This message has been edited by iwire (edited 07-02-2004).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#88646 - 07/02/04 06:52 AM Re: V.F.D. calcs
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
430.6c
If the maximum operating current does not appear on the nameplate ,the ampacity determinated shall be based on 150% of the valves given in tables 430.149 and 430.150.

Top
#88647 - 07/02/04 06:57 AM Re: V.F.D. calcs
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I do not see that 430.6(C) changes the requirments of 430.2
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts