Biding a hair salon print shows lite switches in all the rooms. Owner and builder say it does not need to be like this. what are your thoughts?
Top
2017 / 2014 NEC & Related Books and Study Guides
#88637 - 07/02/04 07:49 AM Re: comercial lite switches
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
In commercial work the NEC does not require any light switches.

However, you may be in an area with energy codes that need to be met, this usually means that the lighting needs to be controlled in some way that will shut it off when not needed, timers, occupancy sensors etc.

The easiest way to comply with this is often the use of motion sensor switches in each room.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#88638 - 07/04/04 10:58 AM Re: comercial lite switches
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Switches, I agree are not required, but unless you have some type of switching means, like a timer, motion control, dimmer or contactor. The only thing left is the CB...


If using Circuit Breakers as a Switch, see:

Quote:
240.83(D) Used as Switches. Circuit breakers used as switches in 120-volt and 277-volt fluorescent lighting circuits shall be listed and shall be marked SWD or HID. Circuit breakers used as switches in high-intensity discharge lighting circuits shall be listed and shall be marked as HID.


Circuit breakers marked SWD are 15- or 20-ampere breakers that have been subjected to additional endurance and temperature testing. New in the 2002 Code, breakers marked with HID are acceptable for switching applications. If high-intensity discharge lighting such as mercury vapor, high-pressure or low-pressure sodium, or metal halide lighting is used, the breaker used for switching must be marked HID


The way this read around my area, is that ALL CB's as switches are to be SWD type. Because fixtures can be changed out without permit.

[This message has been edited by e57 (edited 07-04-2004).]
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#88639 - 07/05/04 04:15 AM Re: comercial lite switches
tomselectrc Offline
Member
Registered: 03/14/04
Posts: 49
Loc: warren mi us
thanxs for the info, can't beleve seperate rooms don't need a switch!
Top
#88640 - 07/05/04 10:48 AM Re: comercial lite switches
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Well, picture a jewlery store, or bank where anyone could walk in and shut off the lights.....
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#88641 - 07/06/04 03:44 PM Re: comercial lite switches
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Tomselectric:

Here in NJ, IF the switches are on the prints submitted for plan review, and issuing of an electrical permit...they shall be installed. The only acceptable way NOT to install them would be a letter (signed and sealed) from the Architect/Engineer of Record stating that it is an approved change.

As Iwire stated...the NEC does not require comm switches, but an energy code, or local (state) regulations may make it mandatory.

I suggest you check with the area AHJ before you get in to deep.

John
_________________________
John
Top
#88642 - 07/08/04 03:53 AM Re: comercial lite switches
tomselectrc Offline
Member
Registered: 03/14/04
Posts: 49
Loc: warren mi us
thanks for the reply,called AHJ told me sumitted plans that have switch should have them.lost bid due to owner not agreeing.think it was better to lose than deal with the owner!
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 41 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals