The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
2 registered (sparkyinak, LongRunner), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#8850 - 04/06/02 03:50 PM Bussman Fuses
GlennH Offline
Member

Registered: 11/15/01
Posts: 39
Loc: pa.
Seeing that Mr. Neeser has entered the fray I have a question for him or anyone else. I had a 750 va control transformer (208-120) with 2 fuseholders on primary side . One on each leg of 208volt. Sticker by fuseholder said to use Littelfuse FLQ-6 fuses. One of the fuses blew for whatever reason, Went to supply house to get some but the only had Bussman type FNQ-6 They said they were equal to FLQ. So put one in and all seemed fine. I now have 1 FLQ-6 and 1 FNQ-6 fuse in (BTW this was in Trane chiller) chiller ran about 30 hrs. and FNQ blew again. Replaced, ran another 30 hrs and blew again. Seemed like an intermitent problem on control circuit. To make short story long, replaced fuseholder, 2 trips by Trane rep ( who said to replace transformer which we did , no difference.) many blown fuses and pulled out hairs. In all this time we never blew the Littelfuse FLQ . Bussman FNQ-6 would blow nearly everytime we would power up transformer. Got more fuses, this time we got Littelfuse FLQ-6 fuses. Guess what ,fuse never blew again. Product literature suggests these two fuses are identical, Both made for high inrush current of transformers. Whats the difference? Bad batch of fuses or ?


Glenn
Charter member CQA
(convoluted questioners of america)

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#8851 - 04/07/02 09:14 AM Re: Bussman Fuses
3rd degree Burns Offline
Member

Registered: 02/04/02
Posts: 38
Loc: Dallas, Texas, USA
Glenn,
Offhand I'd say that although obviously there is a problem, it's not fuse related. After all, the original FNQ-6 did blow and so did its FLQ-6 replacement. I assume this chiller feeder is single-phase 208v. taken off of a 208/120 wye secondary. If this were three phase, I would immediately suspect one of the phases....hang a clamp-on and look for overload, imbalance, etc.

Top
#8852 - 04/12/02 09:55 AM Re: Bussman Fuses
Dan Neeser Offline
Member

Registered: 03/12/02
Posts: 29
Loc: St. Louis, MO, USA
Glenn,

When it comes to time-delay supplemental fuses it can be a little tricky. This is because the fuses have to meet certain performance points as detailed by UL 248. However, outside of those points, fuses from different manufacturers can vary, especially with regards to inrush characteristics.

Because of this some-manufacturers may have more time-delay for inrush considerations than others. This may even change based upon the ampere rating of the fuse and inrush point (or current value) and time duration of inrush spike. This may be the case here and is can be more of an issue for small control transformers because they can have an unusually high inrush.

However, a good comment was made by the previous person...since the FLQ opened maybe there was a problem with the transformer.

In this case, I would probably recommend using the FLQ for this application unless the FNQ can be sized a little higher.

Keep in mind, other applications with the FNQ may not have this issue, it can depend upon the control transformer used.

Thanks,
Dan