The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (NORCAL, sparkyinak), 205 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#88336 - 05/28/04 06:35 PM Tap rules
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Here's the problem: I have a 400 ampere feeder (Fused at 400 amperew) and I'm taping to feed a 40 ampere load using a 60 ampere saftey switch and installing 40 ampere fuses to protect my 40 ampere load conductors. What size wire should I use from the feeder tap to the 60 ampere disconnect? (Using THHN in a damp location).
_________________________
George Little

Top
2014 / 2011 NEC & Related Books and Study Guides
#88337 - 05/28/04 06:36 PM Re: Tap rules
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Forgot to tell you the tap is 8 feet long.
_________________________
George Little

Top
#88338 - 05/28/04 06:46 PM Re: Tap rules
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I would say #8
_________________________
Ryan Jackson,
Salt Lake City

Top
#88339 - 05/28/04 07:02 PM Re: Tap rules
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
George you ask some interesting questions.

Assuming a lot here, but if all the requirements of 240.21(B)(1) are met I agree with Ryan 8 AWG copper.

Now one for you, or anyone, what size grounding conductor is needed from the point of the tap to the 60 amp disconnect?

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#88340 - 05/28/04 09:20 PM Re: Tap rules
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
 Quote:
but shall not be required to be larger than the circuit conductors supplying the equipment.
_________________________
Don(resqcapt19)

Top
#88341 - 05/29/04 02:55 AM Re: Tap rules
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Yes, but the question remains.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#88342 - 05/29/04 05:38 AM Re: Tap rules
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The tap conductors are the conductors feeding the equipment and so the EGC is #8. Table 250.122 requires a #3 EGC for a 400 amp OCPD, but #3 is larger than the conductors feeding the equipment and the EGC is not required to be larger than the conductors feeding the equipment.
Don
_________________________
Don(resqcapt19)

Top
#88343 - 05/29/04 06:31 AM Re: Tap rules
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
IMO a lot of people would size the conductor I am asking about based on the 40 amp fuse which would be 10 AWG copper which will be correct on the load side of that 60 amp disconnect.

I wanted to point out that the EGC on the supply side of the 60 amp disconnect will need to be based on the 400 OCP.

That would normally be a 3 AWG but for this application, will only need to be 8 AWG as the supply conductors are only 8 AWG.

I thought Georges example was perfect for pointing all this out, only a little off topic.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#88344 - 05/29/04 06:37 AM Re: Tap rules
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
FWIW I would wire this disconnect up with 6 AWG, the length is short the difference in price and difficulty will not be a big deal.

Besides all I do is order the stuff, I do not pay for it.

JMO, not required, Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#88345 - 05/29/04 12:51 PM Re: Tap rules
dfe Offline
Member

Registered: 05/25/04
Posts: 18
Loc: n.h. calif. usa
I agree with Iwire
#6 for the full load amps of the 60/as ( in the future you could change the load without rewire the whole mess )
#10 ground
all wire thwn ( damp location )

As long as the total wire lenth of the tap is less then 10'

Top