#88336 - 05/28/04 06:35 PM Tap rules
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Here's the problem: I have a 400 ampere feeder (Fused at 400 amperew) and I'm taping to feed a 40 ampere load using a 60 ampere saftey switch and installing 40 ampere fuses to protect my 40 ampere load conductors. What size wire should I use from the feeder tap to the 60 ampere disconnect? (Using THHN in a damp location).
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#88337 - 05/28/04 06:36 PM Re: Tap rules
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Forgot to tell you the tap is 8 feet long.
_________________________
George Little
Top
#88338 - 05/28/04 06:46 PM Re: Tap rules
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I would say #8
_________________________
Ryan Jackson,
Salt Lake City
Top
#88339 - 05/28/04 07:02 PM Re: Tap rules
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
George you ask some interesting questions.

Assuming a lot here, but if all the requirements of 240.21(B)(1) are met I agree with Ryan 8 AWG copper.

Now one for you, or anyone, what size grounding conductor is needed from the point of the tap to the 60 amp disconnect?

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#88340 - 05/28/04 09:20 PM Re: Tap rules
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
Quote:
but shall not be required to be larger than the circuit conductors supplying the equipment.
_________________________
Don(resqcapt19)
Top
#88341 - 05/29/04 02:55 AM Re: Tap rules
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Yes, but the question remains.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#88342 - 05/29/04 05:38 AM Re: Tap rules
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
The tap conductors are the conductors feeding the equipment and so the EGC is #8. Table 250.122 requires a #3 EGC for a 400 amp OCPD, but #3 is larger than the conductors feeding the equipment and the EGC is not required to be larger than the conductors feeding the equipment.
Don
_________________________
Don(resqcapt19)
Top
#88343 - 05/29/04 06:31 AM Re: Tap rules
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
IMO a lot of people would size the conductor I am asking about based on the 40 amp fuse which would be 10 AWG copper which will be correct on the load side of that 60 amp disconnect.

I wanted to point out that the EGC on the supply side of the 60 amp disconnect will need to be based on the 400 OCP.

That would normally be a 3 AWG but for this application, will only need to be 8 AWG as the supply conductors are only 8 AWG.

I thought Georges example was perfect for pointing all this out, only a little off topic.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#88344 - 05/29/04 06:37 AM Re: Tap rules
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
FWIW I would wire this disconnect up with 6 AWG, the length is short the difference in price and difficulty will not be a big deal.

Besides all I do is order the stuff, I do not pay for it.

JMO, not required, Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#88345 - 05/29/04 12:51 PM Re: Tap rules
dfe Offline
Member
Registered: 05/25/04
Posts: 18
Loc: n.h. calif. usa
I agree with Iwire
#6 for the full load amps of the 60/as ( in the future you could change the load without rewire the whole mess )
#10 ground
all wire thwn ( damp location )

As long as the total wire lenth of the tap is less then 10'
Top
Page 1 of 3 1 2 3 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
2 registered (Admin, HotLine1), 90 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals