The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
sparky 4
Who's Online
0 registered (), 114 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#88294 - 05/27/04 11:09 AM detached building (again) sorry
Reel-Break Offline

Registered: 04/04/02
Posts: 179
Loc: nc
OK ,I have a 200amp service residential.I have a out building/workshop with a 100 amp main breaker panel installed. Now can I run 3 wire service to it?Bond neutral to can.
Do I place a rod there or not?
Do I run 4 wire and place rod?
I re read some past threads but need alittle
reassurance.Thanks in advance.
using direct burial cable pvc conduit.

2014 / 2011 NEC & Related Books and Study Guides
#88295 - 05/27/04 12:44 PM Re: detached building (again) sorry
Ryan_J Offline

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Are there any continuos metal paths between the building? Such as water pipe, gas, coax, phone, etc...?
Ryan Jackson,
Salt Lake City

#88296 - 05/27/04 01:35 PM Re: detached building (again) sorry
Reel-Break Offline

Registered: 04/04/02
Posts: 179
Loc: nc
Not that I`m aware of at this time.I read 250.32 Not clear on the single branch part.Electricians here say you can run three wire but the best way would be go with 4 wire and the rod.Just would like to better understand if three wire is permisable in this situation legally. But also personally I`m lean towards the best way if it is better.

#88297 - 05/27/04 02:04 PM Re: detached building (again) sorry
BPHgravity Offline

Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
If your installing a panelboard at the workshop, than you don't have a single branch circuit going to the workshop, you have a feeder.

Regardless if you wire with 3-wire or 4-wire, a grounding electrode system will be required at the workshop building.

I don't think either way can be classified as "better". Both will provide adequate service and practical safegaurding.
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

#88298 - 06/10/04 02:34 PM Re: detached building (again) sorry
triple Offline

Registered: 04/01/02
Posts: 182
Loc: Wisconsin
Take a course on stray voltage and you will find out why the 4-wire method IS better than using only 3.

If you are not sure of metallic paths then you MUST use 4-wire.

Ground rod(s) are necessary at the second building.