#88294 - 05/27/04 11:09 AM detached building (again) sorry
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 179
Loc: nc
OK ,I have a 200amp service residential.I have a out building/workshop with a 100 amp main breaker panel installed. Now can I run 3 wire service to it?Bond neutral to can.
Do I place a rod there or not?
Do I run 4 wire and place rod?
I re read some past threads but need alittle
reassurance.Thanks in advance.
using direct burial cable pvc conduit.
Top
2017 / 2014 NEC & Related Books and Study Guides
#88295 - 05/27/04 12:44 PM Re: detached building (again) sorry
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Are there any continuos metal paths between the building? Such as water pipe, gas, coax, phone, etc...?
_________________________
Ryan Jackson,
Salt Lake City
Top
#88296 - 05/27/04 01:35 PM Re: detached building (again) sorry
Reel-Break Offline
Member
Registered: 04/04/02
Posts: 179
Loc: nc
Not that I`m aware of at this time.I read 250.32 Not clear on the single branch part.Electricians here say you can run three wire but the best way would be go with 4 wire and the rod.Just would like to better understand if three wire is permisable in this situation legally. But also personally I`m lean towards the best way if it is better.
Top
#88297 - 05/27/04 02:04 PM Re: detached building (again) sorry
BPHgravity Offline
Member
Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
If your installing a panelboard at the workshop, than you don't have a single branch circuit going to the workshop, you have a feeder.

Regardless if you wire with 3-wire or 4-wire, a grounding electrode system will be required at the workshop building.

I don't think either way can be classified as "better". Both will provide adequate service and practical safegaurding.
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Top
#88298 - 06/10/04 02:34 PM Re: detached building (again) sorry
triple Offline
Member
Registered: 04/01/02
Posts: 182
Loc: Wisconsin
Take a course on stray voltage and you will find out why the 4-wire method IS better than using only 3.

If you are not sure of metallic paths then you MUST use 4-wire.

Ground rod(s) are necessary at the second building.
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 89 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals