The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by Trumpy
Today at 05:25 AM
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
ESA Arc flash course
by frank
Yesterday at 04:25 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
0 registered (), 0 Guests and 185 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#88289 - 05/27/04 09:29 AM Panelboard Heights
skingusmc Offline
Member

Registered: 05/27/04
Posts: 116
Loc: Simi Valley, CA USA
Is there a minimum and maximum height for a wall mounted panelboard (service entrance and sub panels)?
_________________________
Thanks
Steve

Top
2017 / 2014 NEC & Related Books and Study Guides
#88290 - 05/27/04 09:49 AM Re: Panelboard Heights
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
6'7" to the heighest breaker, no minimum height specified except for mobile homes.
_________________________
Ryan Jackson,
Salt Lake City

Top
#88291 - 05/27/04 10:24 AM Re: Panelboard Heights
skingusmc Offline
Member

Registered: 05/27/04
Posts: 116
Loc: Simi Valley, CA USA
Ryan_J

Is there a reference I could go to?

Is the 6'7" height the height of the actual top CB or the top of the box?

Thanks
Steve
_________________________
Thanks
Steve

Top
#88292 - 05/27/04 10:33 AM Re: Panelboard Heights
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
404.8 Accessibility and Grouping.
(A) Location. All switches and circuit breakers used as switches shall be located so that they may be operated from a readily accessible place. They shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform.

don
_________________________
Don(resqcapt19)

Top
#88293 - 05/27/04 10:34 AM Re: Panelboard Heights
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
404.8(A)

6'-7" to the center of the operating handle in the highest position.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top