#88281 - 05/26/04 08:31 PM Air Massage tub bonding
mcleodelectric Offline
Junior Member
Registered: 05/26/04
Posts: 3
Loc: Massachusetts, USA
Hi everyone
I am currently on a job where I will need to wire an air blower type massage tub.
The blower motor is double insulated and in a plastic housing, no bonding provisions
are installed (presumably because there is no need to bond the tub).
Am I correcet in assuming all I need to do is provide GFCI protection?

Thanks,
Mike
Top
2017 / 2014 NEC & Related Books and Study Guides
#88282 - 05/27/04 06:24 AM Re: Air Massage tub bonding
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
What is an air massage tub? Is that a hydromassage tub or a theraputic tub? Take a look at 680 and if you can, try to determine exactly what the tub is in code language.
_________________________
Ryan Jackson,
Salt Lake City
Top
#88283 - 05/27/04 05:43 PM Re: Air Massage tub bonding
mcleodelectric Offline
Junior Member
Registered: 05/26/04
Posts: 3
Loc: Massachusetts, USA
Thanks for answering

The tub is similar to a hydromassage tub,
exept it does not pump any water.

In Article 680 definitions this one sort of falls between the cracks.

It only blows air. All electrical components are double insulated. There is nothing to bond. I called the manufacturer today, they said no bonding is required. I also called the Mass board of electrical examiners today for a little guidance, but have not heard back yet.

Any thoughts ?

Mike
Top
#88284 - 05/27/04 05:49 PM Re: Air Massage tub bonding
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
I guess if there is nothing to bond, there is nothing to bond. Do you have any copper water piping? Do you any metallic electrical components that are not double insulated..such as a four sqaure box or a metal faceplate or anything like that?
_________________________
Ryan Jackson,
Salt Lake City
Top
#88285 - 05/27/04 08:02 PM Re: Air Massage tub bonding
mcleodelectric Offline
Junior Member
Registered: 05/26/04
Posts: 3
Loc: Massachusetts, USA
to Ryan_j

Yes, there are copper water lines feeding the tub, but no other metallic parts larger tha 3" in any dimension.

The installation in question is a tub made by Aquatic, Serenity IV Model. It is actually quite clever in design, and seems inherently much safer than any other water pumping tubs (hydromassage) I have seen.

The problem lies with the (ignorance of)some local inspectors. One required the control box have a lug added to it internally and bond the control box to the hot and cold pipes, then run the bond wire into the receptacle box and connect it to the GFCI circuit equipment grounding conductor.

Another said "Nice tub.Nothing here to bond, Huh?", and signed off on the job.

I think somewhere between the two there is a method which will allow me to sleep at night.

thanks again
Mike

[This message has been edited by mcleodelectric (edited 05-27-2004).]
Top
#88286 - 05/27/04 08:09 PM Re: Air Massage tub bonding
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Your welcome

I would be the inspector that said "nothing to bond, huh?"

To add a lug to a double insulated equipmenent violates not only its listing, but 680.74 as well.
_________________________
Ryan Jackson,
Salt Lake City
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals