#88266 - 05/25/04 03:07 PM Grounding Service
ga.sparky56 Offline
Member
Registered: 11/24/02
Posts: 558
Loc: young harris georgia usa
This is a 200a 1ph. UG residential service.

No metallic water lines,interior or exterior. Meterbase is back to back with a 200a main brkr. panel. Short pvc nipple between them. # 4 solid copper from lug in MB down to 2 ground rods 6' apart.

No Ahj here. Homeowner hired a retired elec inspector to look at job and he says the #4 must come from the panel.

Can anyone give me a code art.for this?

Russell
Top
2017 / 2014 NEC & Related Books and Study Guides
#88267 - 05/25/04 03:15 PM Re: Grounding Service
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Hello Russell, It sounds as though this retired inspector is from an area that is not used to seeing this connection at the meter.

Roger

[This message has been edited by Roger (edited 05-25-2004).]
Top
#88268 - 05/25/04 03:29 PM Re: Grounding Service
ga.sparky56 Offline
Member
Registered: 11/24/02
Posts: 558
Loc: young harris georgia usa
Hi Roger.

Thats what I thought. I don't see the difference in this situation.

Russell
Top
#88269 - 05/25/04 06:18 PM Re: Grounding Service
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
Russell,

The connection to a ground rod doesn't need anything larger than #6 Copper. Nothing wrong with the #4 of course.

Peter
_________________________
Peter
Top
#88270 - 05/25/04 06:47 PM Re: Grounding Service
ga.sparky56 Offline
Member
Registered: 11/24/02
Posts: 558
Loc: young harris georgia usa
You're right CT. It's just a habit.

[This message has been edited by ga.sparky56 (edited 05-25-2004).]
Top
#88271 - 05/27/04 08:13 PM Re: Grounding Service
markp Offline
Member
Registered: 04/12/04
Posts: 60
Loc: Kent, WA, USA
Here in Washington, the meter base is not considered to be accessible to the occupant. Technically, the power company says you need to call and coordinate cutting the seal, there its not really accessible. Therefore, the GEC can not be run from there.

This is a AHJ call, and not an NEC code rule except for a strict interpretation of 250.68 which says the GEC must be accessible.
_________________________
Mark
Kent, WA
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 68 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals