The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 54 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#88161 - 05/18/04 04:32 PM "fill calculation" for recept. yoke
sparkync Offline

Registered: 10/17/02
Posts: 811
Loc: NC
I'm doing a house where the homeowner wants everything done in # 12 wire. In figuring the fill calculations, is the entire duplex recept. counted as one yoke, or is each plug in counted as a yoke?? The code says to allow double for each yoke In other words using # 12 wire one duplex outlet would be considered as the following??
2.25 per conductor X 2 ( double for 1 yoke if whole recpt. is considered 1 yoke) = 4.5 cubic inch? Been a while since I had to figure it, and I have a brain freeze
Thanks, Steve

Also I forgot one other thing. On the outside lighting, can you still use a switch box for the outside lighting if it is laid in brick, or does it have to be a light box. Seems like I remember an exception for this rule, that says you can use a switch box, but I'm not sure.. Thanks again.. Steve

[This message has been edited by sparkync (edited 05-18-2004).]

2014 / 2011 NEC & Related Books and Study Guides
#88162 - 05/18/04 04:36 PM Re: "fill calculation" for recept. yoke
Ryan_J Offline

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
The entire device is considered to be one yoke. For example, a single receptacle, a duplex, a triplex, a dimmer, a GFCI, a switch, these are all considered to be a single yoke and therefore a double volume allowance shall be made (2.25*2=4.5).
Ryan Jackson,
Salt Lake City

#88163 - 05/19/04 08:12 AM Re: "fill calculation" for recept. yoke
HotLine1 Offline


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA
Based on the NEC, yes one device (as Ryan stated) counts as two conductors, as you calculated.

The 'common sense' rules that I/we use allow for a little extra room for 'big' devices (GFI, dimmer, etc) Heck, a little extra room never hurts. 22/23 CI plastic new work, 1 gangs are the only 1-gangs we use. Comm is 4x4 deep, or need be a 3-1/2 device, gangable (gem).

With my AHJ hat on, you may be surprized how many 'bof-fill' red stickers are written.


#88164 - 05/19/04 01:34 PM Re: "fill calculation" for recept. yoke
CTwireman Offline

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Why does the homeowner want everything in #12? Seems like a waste of money and resources to me. It's a misconception that wiring everything with #12 minimum is a better system.


#88165 - 05/20/04 06:37 AM Re: "fill calculation" for recept. yoke
velect Offline

Registered: 05/01/04
Posts: 79
Loc: st joseph mi usa
I believe switch boxes can be used for fixtures. As long as the fixture is 6 pounds or less.

#88166 - 05/20/04 10:04 AM Re: "fill calculation" for recept. yoke
macmikeman Offline

Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
That applies to wall mounted fixtures only,(like your situation) just in case someone reads the last post and tries to hang a 5 pound light on the ceiling

#88167 - 05/25/04 07:00 PM Re: "fill calculation" for recept. yoke
sparkync Offline

Registered: 10/17/02
Posts: 811
Loc: NC
Thanks for all the replies. Just now finding a little time to respond. In response to why the homeowner wants it done in #12 wire, is because the rest of his house is in #12. I agree, that # 12 is not necessarily better, especially on lights. Though it will carry more load, heat, etc., it can be damaging to residential switches if care is not taken, plus the overall fill in a box can be tougher on devices when pushing them back in the box etc.... But this is the way he wanted it, and he's the one paying.... I hope I haven't got paid yet. Thanks again for all the responses. I decided to go with metal octagon boxes for the outside lights. He has bought a bunch of lights on sale, and I'm not sure what he's got to put out there. Steve