#88155 - 05/15/04 11:04 AM 210.4
donles Offline
Member
Registered: 04/28/01
Posts: 83
Loc: Pennsylvania
Do I read this article correctly? In a residence, a common disconnect is not required if the circuits do not terminate on the same device or yoke. IOW, I can run 12/3 from two adjacent breakers in the panelboard to a j-box, then split off into two separate 12/2 runs for small appliance circuits? I bet alot of elec's use common trip breakers anyway.
Don
Top
2017 / 2014 NEC & Related Books and Study Guides
#88156 - 05/15/04 11:19 AM Re: 210.4
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Your interpretation is correct except it can also apply to "other" than Dwelling Units, see 210.7(C). The key here is, if we are using a "Multi-Wire circuit it is only one circuit.

Also the breakers do not have to be ajacent to one another, they only have to be on different legs or phases.

Roger
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals