The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 282 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#88077 - 05/07/04 11:52 AM Hospital feeders wiring methods
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Question

Panel feeders to a general care area not on essential electricial system ,PVC allowed???
I know for branch circuits part b applies approved grounding raceway AND insulated grounding condutor But feeders???
All I can find code references to are Branch circuits.

Top
2014 / 2011 NEC & Related Books and Study Guides
#88078 - 05/08/04 04:25 AM Re: Hospital feeders wiring methods
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Yoopersup, yes PVC is allowed for normal feeders. (Equipment branch also)

Since there are no specific requirements like there are for branch circuits, 517.12 allows using wiring methods from chapters 1 thru 4

Roger

Top
#88079 - 05/08/04 11:59 AM Re: Hospital feeders wiring methods
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
517.13(B) says the grounding conductor shall be installed in metal raceways or metal clad cables with the branch circuit conductors. This would imply only back to the panelboard. However,517.13(A) requires a ground path for fault current by a metal raceway system of cable armor assembly.
A ground path for fault current must be continuous to the source of it's supply which in most cases is a transformer and would include the panel feeder.

Top
#88080 - 05/10/04 05:05 AM Re: Hospital feeders wiring methods
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
517.19d Panelboard Grounding Which is a critical area ( I;m talking about is only General care area). Says grounded electrical system is used AND a Metal feeder or raceway OR type mc or mi cables IS installed:::::: So I;m taking it other wiring metods besides metal can be used . This was for Critical and I;m talking about General care. The IS installed again tells me I have other options. Again input is welcomed

Top
#88081 - 05/10/04 06:52 AM Re: Hospital feeders wiring methods
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Yoopersup,
 Quote:
So I;m taking it other wiring metods besides metal can be used .
this is correct.

517.19 doesn't have any bearing in this application, and even if it did, it would allow "Normal" feeders to be installed as you stated in your sentence above.

Roger

Top
#88082 - 05/10/04 07:12 PM Re: Hospital feeders wiring methods
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
I am trying to understand the reason for specifically requiring a redundant path with a metallic raceway from the panel to the devices but falling short of specifically requiring it for the feeder. The way I see it all the electrical redundancy is lost at the panelboard. Like I said above it requires a metallic ground fault path but it appears only from the panel to the device. Not the entire electrical path.

Top