#88077 - 05/07/04 02:52 PM Hospital feeders wiring methods  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
Question

Panel feeders to a general care area not on essential electricial system ,PVC allowed???
I know for branch circuits part b applies approved grounding raceway AND insulated grounding condutor But feeders???
All I can find code references to are Branch circuits.


2017 / 2014 NEC & Related Books and Study Guides

#88078 - 05/08/04 07:25 AM Re: Hospital feeders wiring methods  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Yoopersup, yes PVC is allowed for normal feeders. (Equipment branch also)

Since there are no specific requirements like there are for branch circuits, 517.12 allows using wiring methods from chapters 1 thru 4

Roger


#88079 - 05/08/04 02:59 PM Re: Hospital feeders wiring methods  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
517.13(B) says the grounding conductor shall be installed in metal raceways or metal clad cables with the branch circuit conductors. This would imply only back to the panelboard. However,517.13(A) requires a ground path for fault current by a metal raceway system of cable armor assembly.
A ground path for fault current must be continuous to the source of it's supply which in most cases is a transformer and would include the panel feeder.


#88080 - 05/10/04 08:05 AM Re: Hospital feeders wiring methods  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
517.19d Panelboard Grounding Which is a critical area ( I;m talking about is only General care area). Says grounded electrical system is used AND a Metal feeder or raceway OR type mc or mi cables IS installed:::::: So I;m taking it other wiring metods besides metal can be used . This was for Critical and I;m talking about General care. The IS installed again tells me I have other options. Again input is welcomed


#88081 - 05/10/04 09:52 AM Re: Hospital feeders wiring methods  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Yoopersup,
Quote
So I;m taking it other wiring metods besides metal can be used .
this is correct.

517.19 doesn't have any bearing in this application, and even if it did, it would allow "Normal" feeders to be installed as you stated in your sentence above.

Roger


#88082 - 05/10/04 10:12 PM Re: Hospital feeders wiring methods  
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA
I am trying to understand the reason for specifically requiring a redundant path with a metallic raceway from the panel to the devices but falling short of specifically requiring it for the feeder. The way I see it all the electrical redundancy is lost at the panelboard. Like I said above it requires a metallic ground fault path but it appears only from the panel to the device. Not the entire electrical path. [Linked Image]



Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.7743 MB (Peak: 0.9178 MB) Zlib enabled. Server Time: 2017-03-26 11:04:59 UTC