I have a Contractor who maintains that an acceptable way of bonding/grounding a metal box used in a NM cable installation, would be to wrap the bare equipment ground wire around the screw that is used with the cable clamp. Now there are no cables under the clamp and the clamp is still installed so the bare wire is under the head of the screw and between the screw head and the clamp. I maintain that the Contractor should be using the 8-32 hole provided for installing a GREEN screw and not use the cable clamp screw what-so-ever for grounding. I don't think he should even use the silver colored cable clamp screw in the hole provided for the GREEN ground screw. I need something official for a reference. Thank You in advanc.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#87937 - 05/05/04 06:03 AM Re: Need opinion
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
George
Look at 250.148A
Top
#87938 - 05/05/04 06:07 AM Re: Need opinion
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
George also 314.40D
Top
#87939 - 05/05/04 06:31 AM Re: Need opinion
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
There is no code rule that requires the use of a "green" screw for the connection of the EGC. The use of the clamp screw with the clamp still installed would be a violation of 250.148(A), but there is no violation if the clamp is removed and the clamp screw is used to connect the EGC.
Don
_________________________
Don(resqcapt19)
Top
#87940 - 05/05/04 12:59 PM Re: Need opinion
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
250.148A says a GROUNDING screw used for NO other purpose! A box clamp screw is Not a Grounding screw. For one thing the head is usually to small and the wire tends to slip out when tightened.
Top
#87941 - 05/05/04 02:55 PM Re: Need opinion
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Yoopersup: I concur with Don. What is to prevent you from using a Sta-Con from satisfying your dilemna?
_________________________
Ryan Jackson,
Salt Lake City
Top
#87942 - 05/05/04 04:40 PM Re: Need opinion
hbiss Offline
Member
Registered: 12/16/03
Posts: 886
Loc: Hawthorne, NY USA
...Now there are no cables under the clamp and the clamp is still installed so the bare wire is under the head of the screw and between the screw head and the clamp.

Why the heck would you leave an unused clamp in the box anyway? Not only would it prevent the screw from being firmly tightened on the ground wire and is a violation of 250.148(A) but it counts as a conductor in calculating box fill.

Dunno, but whenever I see unused clamps still in place it screems DIY!

-Hal
_________________________
www.myphonetechs.com
Top
#87943 - 05/05/04 08:06 PM Re: Need opinion
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
I agree with Don and Ryan. There is no definition of a ground screw in the NEC. The usual mentioning of a green hex head screw is for devices 250 126. Yoopersup has provided two good references.

Pierre
_________________________
Pierre Belarge
Top
#87944 - 05/06/04 08:24 AM Re: Need opinion
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Yoopersup,
Please show me the NEC definition of a "grounding screw".
Don
_________________________
Don(resqcapt19)
Top
#87945 - 05/06/04 10:02 AM Re: Need opinion
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
I believe there is no UL listing for ground screws only.

The only UL Listed screw items I have ever seen are a combination of screw and wire pig tail.
Top
Page 1 of 12 1 2 3 11 12 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 40 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals