The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 198 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87925 - 05/04/04 10:35 AM Underground Wiring
coulomb Offline
Junior Member

Registered: 05/04/04
Posts: 1
Loc: Erie, PA, USA
I would like to install underground wiring along a long curved driveway for very low profile light fixtures (path lighting). I don't want to stub up PVC 90 degree ells into above ground junction boxes. Can PVC
"T" fittings be buried and used as junction
boxes? What are my code approved options here? The driveway is 250 feet long and the fixtures will be 25 feet apart. Thanks!

Top
2014 / 2011 NEC & Related Books and Study Guides
#87926 - 05/04/04 11:25 AM Re: Underground Wiring
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
You really can not bury J-boxes or conduit bodys ("T"s)

 Quote:
314.29 Boxes and Conduit Bodies to Be Accessible.
Boxes and conduit bodies shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade.

Exception: Listed boxes shall be permitted where covered by gravel, light aggregate, or noncohesive granulated soil if their location is effectively identified and accessible for excavation.


The exception gives you a little leeway , but the box will have to be listed for direct burial.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#87927 - 05/04/04 01:59 PM Re: Underground Wiring
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
That is darn little leeway, I can only think of one type of box that is listed for being installed in the ground & it is large & expensive.

How about Type UF cable? UF could be run up a post. There is a non-metallic post on the market that will conceal the cable where it comes up and the fixture can attach right to the post & it is available in a fairly low profile.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.