#87919 - 05/03/04 02:09 PM Cathodic Protection
rapahoe Offline
Junior Member
Registered: 05/03/04
Posts: 3
Loc: Portland, Or.
I have a new 300 kVA, 12.47kVwye - 480Vwye service transformer for a petroleum distribution facility that has existing cathodic protection system on underground pipelines. Local inspector has given verbal approval to use a cathodic isolation (PCR)module between neutral & grnd of service entrance to satisfy 250-6(e)and block the injected DC. Any special concerns for ground grid under pad mounted transformer or under the service entrance building (14' x 8') less than 10 ft. away?
Thanks!
Top
2017 / 2014 NEC & Related Books and Study Guides
#87920 - 05/04/04 02:17 PM Re: Cathodic Protection
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Cathodic protection is its own beast so far a NEC-type systems are involved. Is it safe to assume that the 300kVA transformer is under the domain of the petrochem and not an electric utility? You might start by scrutinizing the listing instructions and, as needed, contact the “PCR-module” manufacturer for resolution. If this is new territory for the inspection authority, he may be easiest to work with if you approach him up front with as much PCR-specific application information as possible.




[This message has been edited by Bjarney (edited 05-04-2004).]
Top
#87921 - 05/04/04 02:23 PM Re: Cathodic Protection
rapahoe Offline
Junior Member
Registered: 05/03/04
Posts: 3
Loc: Portland, Or.
BJarney - Thanks! I have an inquiry in to the PCR manufacturer regarding grounding concerns and have provided a data package to the inspector. I was hoping to link up with someone else who had worked with the nuts and bolts of this sort of installation.
Top
#87922 - 05/04/04 03:13 PM Re: Cathodic Protection
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
rapahoe — I didn’t mean to lead you astray and pretend I was any sort of CP whiz. I’ve found the “Leister golfcart battery chargers” in rural areas and see them indicating ~50 amperes DC disappearing into the ground over a set of mysterious cables.

One author of CP-application papers is John P Nelson in Colorado, with some online PDFs available at www.neiengineering.com/papers/papers.html
Top
#87923 - 05/04/04 03:42 PM Re: Cathodic Protection
rapahoe Offline
Junior Member
Registered: 05/03/04
Posts: 3
Loc: Portland, Or.
Bjarney, Thanks for the link to John's web site. I had the priviledge of meeting him in Denver a couple years ago.
Top
#87924 - 05/04/04 04:08 PM Re: Cathodic Protection
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
[I’m not sure I would recognize a ‘Little FINK’ test station if I tripped over it.]
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 91 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals