#87841 - 04/22/04 01:38 PM Article 408.15
Doug Scott Offline
Member
Registered: 02/05/03
Posts: 24
Loc: Jonesville, Michigan, USA
I have a 30 circuit 100 amp MB panel. Have a total of 36 cicuits installed using 7 piggyback breakers. Was kicked down on inspection for overloading the panel. Panel does not state that piggyback breakers cannot be used.
Would this fall under Article 408.15 (2002)?
Doug
Top
2017 / 2014 NEC & Related Books and Study Guides
#87842 - 04/22/04 01:55 PM Re: Article 408.15
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
408.15 will not kick in until you get to 42 breakers (43 with your main)

Quote:
Panel does not state that piggyback breakers cannot be used.


It shouldn't it has to tell you how many are allowed if any.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#87843 - 04/22/04 02:09 PM Re: Article 408.15
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
may i join in this one ??


ok i did look at the NEC 96 edition. old art. 384-15

" Number of overcurrent devices on one panelboard"
Not more than 42 overcurrent devices [other than those provided for in the mains] of a lighting and appliance branch-circuit panelboard shall be installed in any one cabient or cut out box.
A lightingand appliance branch-circuit shall be provided with physical means to prevent the installation of more over current devices than that number for which the panelboard was designged, rated, and approved.


so in my option here most imporat part that should read the breaker box label for listing for the numbers and types of breakers that approved for that usage

if i am off track let me know then i can correct my mistake here.

merci, marc

p.s. i did look at my french electrical codes and they say the same thing too.
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#87844 - 04/22/04 05:38 PM Re: Article 408.15
Sparkeee32 Offline
Member
Registered: 03/23/04
Posts: 32
Loc: Federal Way WA USA
I would like to know the theoretical loads these circuits might have. For instance, are you running lots of 20 amp circuits, electric heaters, hot water heater, electric range.... or is everything gas, and you just have alot of lighting circuits? I have a feeling this is not about the # of breakers in the panel, but the size of all the conductors and the ampacities flowing through the said breakers. Some more specifics would be nice! Thanx! Brian!
Top
#87845 - 04/22/04 05:49 PM Re: Article 408.15
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Sparkeee24, you can have as many breakers as you want on a feeder, all that matters is the calculated load.

I have a 126 - 20 amp breakers on a 3 phase 225 amp triple tub panel at the job I am doing now, added up that would be 2520 amps. In reality it is drawing a total of 150 amps (50 per phase)
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#87846 - 04/22/04 10:39 PM Re: Article 408.15
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
Doug, if possible please post the catalog number of the panel.

Curt
_________________________
Curt Swartz
Top
#87847 - 04/23/04 04:13 AM Re: Article 408.15
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma
I seem to recall somewhere a panel that was rated for a certain total rating of all of the breakers attached to it. I don't remember which, and I don't see why (if the calculated load and the feeder rating is less than the ampacity of the bars, who cares what the total of the CB ratings is), but if that is the listing, then that is the listing.

I have also seen panels where the instructions specifically limited the total rating of CBs connected to a single stab on the bus. This is more reasonable, since the rating of the stab might be less than that of the entire bus.

-Jon
Top
#87848 - 04/23/04 02:04 PM Re: Article 408.15
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
You are permitted to use all the spaces in a panelboard in accordance with its listing. If you have a 20/40 panelboard, you may use all the spaces and all of the circuit breakers may be ½" breakers.
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#87849 - 04/26/04 02:21 AM Re: Article 408.15
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
This is a listing and labeling issue - 110.3(B). If the label lists this panel for a maximum of 30 ckts, that is all that is permitted. Reading the label will tell you if you are permitted to have more than 30 ckts (breakers).

Pierre
_________________________
Pierre Belarge
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals