#87648 - 04/01/04 05:26 PM wireway
big guy Offline
Member
Registered: 12/19/03
Posts: 59
Loc: pa
I have seen this done and can't find any
violations.Can you put EMT through a wireway
at a right angle
Example
If i have a panel with a wireway above it (horizontal)can i run EMT Vertically through
the wireway right into the panel.
thanks big guy
Top
2017 / 2014 NEC & Related Books and Study Guides
#87649 - 04/02/04 02:06 AM Re: wireway
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I do not know any violation with that.

Looks bad but sometimes the only option.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#87650 - 04/03/04 06:39 PM Re: wireway
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
725.55(C) permits raceways within enclosures. I do not see where this is prohibited, and as Bob has said may be the only way to reach a panel.

Pierre
_________________________
Pierre Belarge
Top
#87651 - 04/03/04 09:04 PM Re: wireway
stamcon Offline
Member
Registered: 03/24/01
Posts: 329
Loc: So San Francisco CA
Top
#87652 - 04/06/04 02:58 PM Re: wireway
big guy Offline
Member
Registered: 12/19/03
Posts: 59
Loc: pa
yes that is what i has talking about
Would you use the O.D of the pipe as your
20%. 376.22 02 code thanks
Top
#87653 - 04/09/04 08:48 AM Re: wireway
Cobtronics Offline
Member
Registered: 07/24/03
Posts: 18
Loc: Vermont
We do this all the time in the plant I'm in. Many advantages: 1)Makes for a snap to add new pipes in limited spaces. 2) Can run new pipe and wire into gutter w/o shutting down the panel - only shut down for final pull and connect. 3) You run outta KOs on the top fast and the pipe job gets ugly when you have to snake 15 - 20 runs into the side KOs - even pull ells don't help sometimes. On jobs where this wasn't done, the panel top might have been made of chicken wire for all the strength it had after it was punched.
We deduct the volume of the pass thrus from the volume of the box for fill calcs, but that is the engineer's or AHJ's call to make initially.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals