The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 299 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87648 - 04/01/04 05:26 PM wireway
big guy Offline

Registered: 12/19/03
Posts: 52
Loc: pa
I have seen this done and can't find any
violations.Can you put EMT through a wireway
at a right angle
If i have a panel with a wireway above it (horizontal)can i run EMT Vertically through
the wireway right into the panel.
thanks big guy

2014 / 2011 NEC & Related Books and Study Guides
#87649 - 04/02/04 02:06 AM Re: wireway
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I do not know any violation with that.

Looks bad but sometimes the only option.
Bob Badger
Construction & Maintenance Electrician

#87650 - 04/03/04 06:39 PM Re: wireway
PCBelarge Offline

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
725.55(C) permits raceways within enclosures. I do not see where this is prohibited, and as Bob has said may be the only way to reach a panel.

Pierre Belarge

#87651 - 04/03/04 09:04 PM Re: wireway
stamcon Offline

Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA

#87652 - 04/06/04 02:58 PM Re: wireway
big guy Offline

Registered: 12/19/03
Posts: 52
Loc: pa
yes that is what i has talking about
Would you use the O.D of the pipe as your
20%. 376.22 02 code thanks

#87653 - 04/09/04 08:48 AM Re: wireway
Cobtronics Offline

Registered: 07/24/03
Posts: 16
Loc: Vermont
We do this all the time in the plant I'm in. Many advantages: 1)Makes for a snap to add new pipes in limited spaces. 2) Can run new pipe and wire into gutter w/o shutting down the panel - only shut down for final pull and connect. 3) You run outta KOs on the top fast and the pipe job gets ugly when you have to snake 15 - 20 runs into the side KOs - even pull ells don't help sometimes. On jobs where this wasn't done, the panel top might have been made of chicken wire for all the strength it had after it was punched.
We deduct the volume of the pass thrus from the volume of the box for fill calcs, but that is the engineer's or AHJ's call to make initially.