#87615 - 03/25/04 07:12 PM Please see Generator hook up in General Discussions
ayrton Offline
Member
Registered: 12/21/01
Posts: 201
Loc: Pa
I have a building with 2 services. One single phase and one three phase.
1phase service is fed w/250's which are tapped to 4/0 which go through a 200a meter socket than remain 4/0 to a 400a breaker.
All though 4/0 to breaker is obviously wrong, the load of the building is about 180a, hence the 200a meter socket.

My associate/friend who owns a generator service business, has used other electricians in the past and says that "we" do it all the time , meaning use a three phase generator, running conductors to a three phase transfer switch, and than using two of the legs for the single phase, and the three for the three phase.
Only thing we need to power with the three phase is a 70a disc for hvac.
I do not see anything in Art700 pertaining to this. My logic is telling me this shouldnt be done. Need advise

[This message has been edited by ayrton (edited 03-26-2004).]
Top
2017 / 2014 NEC & Related Books and Study Guides

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals