The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 185 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87556 - 03/17/04 06:05 AM New code rule ????
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Hey have I missed something. I put a 100a service on a barn/shop in a neighbooring county.Home owner had all permits of coarse. Well the service is back to back but I installed pvc between meter base and panel AJH tells home owner I must have 4 wire because of pvc.. to bond around the pvc pipe he provided no reference?I put a call in to him this am but haven`t recieved call back.

Top
2014 / 2011 NEC & Related Books and Study Guides
#87557 - 03/17/04 06:47 AM Re: New code rule ????
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Nope, you haven't missed anything, I think. I am assuming that the meter can is bonded to the grounded conductor as allowed by 250.92(B)(1), and the main disconnect is in the barn, not outside. On the load side of the grounded conductor connection point required by 250.24(A)(1), 4 wires would be required.
Which do you have?
_________________________
Earl

Top
#87558 - 03/17/04 07:22 AM Re: New code rule ????
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
If I understand correctly the inspector is wrong. The Grounded Conductor and Equipment Grounding Conductor will be in parallel if you were to do as he suggest. This is unless you were to treat this "Service Equipment" as a "Sub Fed Panel" (which it is not) and isolate the "Grounded Conductor" and "Equipment Grounding Conductor" in the Service Equipment".

The proper way to do this is to install the factory bonding jumper in the panel and the Grounded Conductor would be all that is needed from poco transformer to this point.

The GEC connection can be in the meter (if allowed by Poco) or the Service Equipment. (panel)

Roger

Top
#87559 - 03/17/04 10:31 AM Re: New code rule ????
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Point of info. If it was SE cable would a ground wire be required, NO. So pvc NO

Top
#87560 - 03/17/04 05:19 PM Re: New code rule ????
OreElect Offline
Member

Registered: 03/05/04
Posts: 96
Loc: Salem,Oregon.USA
Two or more services supplied from a common service.
250.32 (B) (1) 4 wire


250.32 (b) (2) 3 wire

Top
#87561 - 03/17/04 05:26 PM Re: New code rule ????
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
OreElect, welcome to the forum.

The first post (as worded) is describing an individual (stand alone) service for the structure.

Roger

Top
#87562 - 03/18/04 05:17 AM Re: New code rule ????
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Hey all is well. The real electrical inspector wasn`t avalible it was a stand in the works for the town he was confused about it being sub panel since the home already had a service. He didn`t see the meter can I guess...(lol)Had me worried You know kinda like you do something and all of a sudden there`s a new interpetation.Thanks for the help.