#87499 - 03/13/04 07:26 PM Wires in canopy?
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I've always enforced the need for a properly sized J-box for splicing fixture wires to the branch circuit conductors and not permitted the installer to rely on the canopy for this purpose. Am I wrong?
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#87500 - 03/14/04 05:44 AM Re: Wires in canopy?
electure Offline


Member
Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Up to 4 #14 or smaller fixture wires aren't counted in box fill anyway, so a box that is properly sized for the branch circuit conductors is sufficient. See 314.16 (B)(1) Exception.

410.10 Space for Conductors
Canopies and oulet boxes taken together shall provide adequate space so that luminaire (fixture) conductors and their connecting devices can be properly installed.
The italics are mine.
Top
#87501 - 03/14/04 12:15 PM Re: Wires in canopy?
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Thanks for your insight. I guess I'll will take a different view of this subject thanks for the code reference. I still am kinda nervous about allowing someone to install a 3" pan box with two 14/2 w/g for connection of a luminaire. I think I'll ask him for some specs on the proposed fixture, I'm sorry, luminaire.
_________________________
George Little
Top
#87502 - 03/14/04 01:27 PM Re: Wires in canopy?
caselec Offline
Member
Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
George

The exception that Scott (electure) posted above applies to the fixture wires not the branch circuit conductors. Using a 3/0 pancake box with even one 14-2 NM cable is a violation unless the box is extended with an extension ring or canopy that is marked with its cubic inch capacity. I have never seen a fixture canopy that has been marked with its capacity. A single 14-2 NM cable would require a minimum of 6 cubic inches if an external clamp is used or 8 cubic inches if an internal clamp is used. A 3/0 pancake has a 4 cubic inch capacity. Two 14-2 NM cables would require 10 cubic inches with internal clamps or 12 cubic inches with internal clamps.

Curt
_________________________
Curt Swartz
Top
#87503 - 03/14/04 07:17 PM Re: Wires in canopy?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
When I inspect I allow (1) 14-2 NM cable in a 3-0 pancake box. I realize that it is not permitted, but I also realize that sometimes that is the only way you can go about the installation. I will not, however, allow (2) 14-2's or (1) 12-2.
_________________________
Ryan Jackson,
Salt Lake City
Top
#87504 - 03/23/04 06:01 PM Re: Wires in canopy?
triple Offline
Member
Registered: 04/01/02
Posts: 182
Loc: Wisconsin
Actually, electure, those four fixture wires you refer to have to be SMALLER than #14 (not "14 or smaller") in order to avoid using them in fill calculations. See: 314.16(B)(1)
Top
#87505 - 03/24/04 03:33 PM Re: Wires in canopy?
Jim M Offline
Member
Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
Ryan,

Why don't they use 4" pancake boxes instead of the 3". I have only seen the 3" on very old work like K&T. Is this a regional thing?
Top
#87506 - 03/24/04 04:37 PM Re: Wires in canopy?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Hi Jim. I wish I could answer your question, but I'm afraid that it is a question I also ask. I can't figure it out. :0
_________________________
Ryan Jackson,
Salt Lake City
Top
#87507 - 03/26/04 08:56 PM Re: Wires in canopy?
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
If the installation of a 4 inch canopy on a 3 inch box is performed where the surface is combustible, it is a violation of 410.13.

Pierre
_________________________
Pierre Belarge
Top
#87508 - 03/27/04 08:53 AM Re: Wires in canopy?
electure Offline


Member
Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Triple,
Thank You! Sometimes I suffer from "Hoof in Mouth" disease.

Smaller than #14...S
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Ruben Rocha), 142 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals