The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 393 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87414 - 03/05/04 10:37 AM Hight voltage clearences
Yoopersup Offline

Registered: 03/04/03
Posts: 826
Loc: Michigan
Where would one find info on the clearence required for a 4160 high voltage utilty line over the roof of a building(industrial) paper mill.There thinking of adding an Addition and the current line would run over the addition. Yes I know some well say contact the utilty company, But its gotta be somewhere.(located in michigan)

2014 / 2011 NEC & Related Books and Study Guides
#87415 - 03/05/04 11:29 AM Re: Hight voltage clearences
George Corron Offline

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
This is a lousy answer, but you can find it in Artlicle 234 of the National Electrical Safety code, but you have to know your cable type, wind load, etc to calculate.

Article 110 and 490 of the NEC do not really address any specifics of 4,160. OSHA is very concerned where there is access to the roof. Will there be equipment requiring service up there? If so, I suggest the minimum is 10 feet which is the minimum clearance for working unless trained, and properly PPE'd.

Hope this gives you an idea where to start.

#87416 - 03/05/04 06:06 PM Re: Hight voltage clearences
OreElect Offline

Registered: 03/05/04
Posts: 96
Loc: Salem,Oregon.USA
clearances;225.60 Over 600v
230.24 not over 600v

#87417 - 03/06/04 07:42 AM Re: Hight voltage clearences
Bjarney Offline

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
FWIW, there is a regional 'NESC-like' document at {2.5MB pp.441}