The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 238 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87401 - 02/26/04 04:21 PM switchboard rating and overcurrent protection
VivaEspana Offline
Junior Member

Registered: 02/26/04
Posts: 1
Loc: Roseville, CA, USA
If the distribution section bus is rated at 1200 amps maximum, period, then is it properly protected per code by a fully rated 1200 amp breaker that doesn't trip on an overcurrent until it reaches 1200 amps?

thanks for your input.

Top
2014 / 2011 NEC & Related Books and Study Guides
#87402 - 02/26/04 05:34 PM Re: switchboard rating and overcurrent protection
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Based on the wording of your question, In my opinion, yes the dist. section is properly protected.

John
_________________________
John

Top