In parallel wiring, when sizing the ground,do you parallel the ground and figure each ground at full rating. In other words, if you have parallel 350s to give you 600 amps, do you pull each ground rated at 600 amps, or do you figure each at 300 amps. I would think you would figure each at 600 amps for full protection. This is for grounding raceway and equipment.
Top
2017 / 2014 NEC & Related Books and Study Guides
#87372 - 02/23/04 06:20 PM Re: Parellel wiring
Jim Phillips Offline
Junior Member
Registered: 02/22/04
Posts: 2
Loc: Canton, Ohio U.S.A.
NEC 250.122(F)(1) Size them based on the upstream overcurrent device as shown in Table 250.122. i.e 600A = minimum #1 Copper

Jim
Top
#87373 - 02/24/04 09:23 AM Re: Parellel wiring
Wirenuttt Offline
Member
Registered: 11/10/02
Posts: 267
Loc: Massachusetts
Thanks Jim;
That was exactly what I needed.

~Andy
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 59 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals