#87349 - 02/18/04 06:04 AM Voltage drop 4160
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Question
formula for voltage drop
example 4160 mtr. distance 475 ft. full load amp (500hp) 70 . Copper wire.
22.3x distance x amps divided circular mil of cooper wire.
22.3x475x70=741477
#4=41740area cir. mills
741477divided by 41740=17.76 voltage drop
4160x3%=124.8
hows it look guys????
Top
2017 / 2014 NEC & Related Books and Study Guides
#87350 - 02/18/04 01:16 PM Re: Voltage drop 4160
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
I prefer the formula VD = 1.73xLxIxR/1,000. The R is resistance per 1,000 feet from Table 9 of Chapter 9. L is the distance from the source to the load in feet. Note that the impedance varies with the pipe type. But is not significant except with higher ampacities. For your parameters using PVC conduit I get: VD = 1.73x475x70x0.31/1,000 = 17.83 volts. Pretty close.
Use 2 instead of 1.73 for single phase.

Earl
_________________________
Earl
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals