#87343 - 02/16/04 11:35 AM mtr amps 4160 volts
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Where do I find a Chart giving full load amps for 4160 volt mtrs. from say 100hp to 1000 hp???
Top
2017 / 2014 NEC & Related Books and Study Guides
#87344 - 02/16/04 02:30 PM Re: mtr amps 4160 volts
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
For 4000V motors [usual nameplate for motors used in 4160V systems] you could use 58% of the 2300V column currents in NEC Table 430-150 3ø Motor Full-Load Current (60-500hp.) Or, using the kVA/hp equivalent, a 100hp 4kV motor would be about 14½ amps and a 1,000hp motor would be ~144 amps.
Top
#87345 - 02/17/04 11:42 AM Re: mtr amps 4160 volts
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
I've always used .14 times Hp. But wondered if theres a chart I could get awhole of.
Top
#87346 - 02/17/04 03:59 PM Re: mtr amps 4160 volts
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
Manufacturer-specific info at www.baldor.com/pdf/brochures/BR435.pdf
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals