The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
51 minutes 42 seconds ago
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
renosteinke 6
ghost307 6
Potseal 4
Who's Online
0 registered (), 277 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87304 - 02/09/04 03:44 PM x-frmr secondary protection??
Edward Offline

Registered: 12/14/02
Posts: 309
Loc: California
I am installing a Buck&Boost transformer. Do i need to have a secondary OCPD.I tried to find it in the 1999 handbook(nec) no luck.

When does an installation require secondary protection?


2014 / 2011 NEC & Related Books and Study Guides
#87305 - 02/09/04 03:49 PM Re: x-frmr secondary protection??
Ryan_J Offline

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
You will probably only have to supply overcurrent protection on the primary side. 450.6(A) and (B) discuss a couple of instances in which secondary OCPD's are required.
Ryan Jackson,
Salt Lake City

#87306 - 02/09/04 03:55 PM Re: x-frmr secondary protection??
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Buck Boosts are autotransformer's and are only required to have primary protection.

450-4(a) 1999 or 2002
Bob Badger
Construction & Maintenance Electrician

#87307 - 02/09/04 04:02 PM Re: x-frmr secondary protection??
Bjarney Offline

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
They're covered in 99NEC 450-4(a) Autotransformers… Secondary overcurrent protection is generally not required, but also note when “secondary” [shunt] OCP is prohibited.

[This message has been edited by Bjarney (edited 02-09-2004).]