The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Yesterday at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
1 registered (geoff in UK), 205 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87304 - 02/09/04 03:44 PM x-frmr secondary protection??
Edward Offline
Member

Registered: 12/14/02
Posts: 309
Loc: California
I am installing a Buck&Boost transformer. Do i need to have a secondary OCPD.I tried to find it in the 1999 handbook(nec) no luck.

When does an installation require secondary protection?

Merci
Edward.
_________________________
Thanks
Edward

Top
2014 / 2011 NEC & Related Books and Study Guides
#87305 - 02/09/04 03:49 PM Re: x-frmr secondary protection??
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
You will probably only have to supply overcurrent protection on the primary side. 450.6(A) and (B) discuss a couple of instances in which secondary OCPD's are required.
_________________________
Ryan Jackson,
Salt Lake City

Top
#87306 - 02/09/04 03:55 PM Re: x-frmr secondary protection??
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Buck Boosts are autotransformer's and are only required to have primary protection.

450-4(a) 1999 or 2002
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#87307 - 02/09/04 04:02 PM Re: x-frmr secondary protection??
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
They're covered in 99NEC 450-4(a) Autotransformers… Secondary overcurrent protection is generally not required, but also note when “secondary” [shunt] OCP is prohibited.




[This message has been edited by Bjarney (edited 02-09-2004).]