The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
01/19/17 09:52 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
0 registered (), 0 Guests and 174 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87304 - 02/09/04 03:44 PM x-frmr secondary protection??
Edward Offline
Member

Registered: 12/14/02
Posts: 309
Loc: California
I am installing a Buck&Boost transformer. Do i need to have a secondary OCPD.I tried to find it in the 1999 handbook(nec) no luck.

When does an installation require secondary protection?

Merci
Edward.
_________________________
Thanks
Edward

Top
2017 / 2014 NEC & Related Books and Study Guides
#87305 - 02/09/04 03:49 PM Re: x-frmr secondary protection??
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
You will probably only have to supply overcurrent protection on the primary side. 450.6(A) and (B) discuss a couple of instances in which secondary OCPD's are required.
_________________________
Ryan Jackson,
Salt Lake City

Top
#87306 - 02/09/04 03:55 PM Re: x-frmr secondary protection??
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Buck Boosts are autotransformer's and are only required to have primary protection.

450-4(a) 1999 or 2002
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#87307 - 02/09/04 04:02 PM Re: x-frmr secondary protection??
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
They're covered in 99NEC 450-4(a) Autotransformers… Secondary overcurrent protection is generally not required, but also note when “secondary” [shunt] OCP is prohibited.




[This message has been edited by Bjarney (edited 02-09-2004).]

Top