The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Ruben Rocha
Today at 07:36 PM
ESA Arc flash course
by frank
Today at 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 27
HotLine1 21
Ruben Rocha 16
Trumpy 12
ghost307 12
Who's Online
1 registered (Trumpy), 0 Guests and 221 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87281 - 02/05/04 06:53 AM Emergency Tap
drillman Offline
Member

Registered: 03/24/03
Posts: 97
Loc: Somewhere in Texas
Found a 100 amp emergency panel fed from a tap of parallel feeders.

The feeders are two sets of 3 ought in two - 2 inch pipes. These have a 350 amp breaker on them.

The tap was made in a pullbox using those piercing type things.

They tapped one set of feeders with #6 wire and ran it about 20 to 30 feet to a panel with an 100 amp main breaker. Did a clamp on test with everything on and theres about 25 amps on each phase.

The panel is mounted above a 30 kva transformer right in front of it. This is funny because 5 feet away there is a clear space.

Plus, the neutral bus of the hacked in emergency panel is connected to the neutral bus on the normal panel.

I told the boss that you cannot tap one side of a parallel feed as it creates an imbalance and that we would need to buy a breaker to refeed the panel and disconnect the tap. Yes, there is room in the main emergency panel for another 3 breakers if needed.

Am I right?

Just want to be sure I am not telling the boss something that will bite me later. Keep in mind my boss is a supervisor with a mangement degree not a technical guy. This is actually good.

The thing about this is that someone went to a lot of trouble to do a lousy job.

Top
2017 / 2014 NEC & Related Books and Study Guides
#87282 - 02/08/04 05:36 AM Re: Emergency Tap
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
You are right

Earl