The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 109 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87281 - 02/05/04 06:53 AM Emergency Tap
drillman Offline
Member

Registered: 03/24/03
Posts: 97
Loc: Somewhere in Texas
Found a 100 amp emergency panel fed from a tap of parallel feeders.

The feeders are two sets of 3 ought in two - 2 inch pipes. These have a 350 amp breaker on them.

The tap was made in a pullbox using those piercing type things.

They tapped one set of feeders with #6 wire and ran it about 20 to 30 feet to a panel with an 100 amp main breaker. Did a clamp on test with everything on and theres about 25 amps on each phase.

The panel is mounted above a 30 kva transformer right in front of it. This is funny because 5 feet away there is a clear space.

Plus, the neutral bus of the hacked in emergency panel is connected to the neutral bus on the normal panel.

I told the boss that you cannot tap one side of a parallel feed as it creates an imbalance and that we would need to buy a breaker to refeed the panel and disconnect the tap. Yes, there is room in the main emergency panel for another 3 breakers if needed.

Am I right?

Just want to be sure I am not telling the boss something that will bite me later. Keep in mind my boss is a supervisor with a mangement degree not a technical guy. This is actually good.

The thing about this is that someone went to a lot of trouble to do a lousy job.

Top
2014 / 2011 NEC & Related Books and Study Guides
#87282 - 02/08/04 05:36 AM Re: Emergency Tap
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
You are right

Earl