#87195 - 01/29/04 03:56 AM 680.22(A)(4)
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
i have a basement pool job. the gfi receptacle's furthest distance is 6' from the pool edge {which i'll feed via gfi breaker, as all the lighting switches are also there 680.22(B)(4)}

this was built this way, not an afterthought, just checking if i'm kosher here i guess...

680.22(A)(4) Restricted Space. Where a pool is within 3.0 m (10 ft) of a dwelling and the dimensions of the lot preclude meeting the required clearances, not more than one receptacle outlet shall be permitted if not less than 1.5 m (5 ft) measured horizontally from the inside wall of the pool.


HB commentary;

The receptacles within the structure are permitted to be less than 10 ft from the pool. Where this installation is at a dwelling unit, it is necessary to provide at least one receptacle between 10 ft and 20 ft from the inside walls of the pool

~S~
Top
2017 / 2014 NEC & Related Books and Study Guides
#87196 - 01/29/04 06:09 AM Re: 680.22(A)(4)
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
The commentary you quoted does not apply to the code section noted. If your lot precludes the receptacle from being installed between 10 and 20 feet from the pool, then it is permissible to install a receptacle between 5 and 10 feet to satisfy 680.22(A)(3).

Earl

I think (4) should be made a subsection of (3), as it applies only to that sub-section.
_________________________
Earl
Top
#87197 - 01/30/04 01:36 PM Re: 680.22(A)(4)
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
thanks Earl but....
Quote:
Where a pool is within 3.0 m (10 ft) of a dwelling and the dimensions of the lot

does this apply to inside a dwelling as well as outside?

~S~
Top
#87198 - 02/01/04 06:31 AM Re: 680.22(A)(4)
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
Sparky
That is a good question. My opinion is the restricted lot requirements would conform to this pool, but I am not your AHJ. I would ask him to be sure.

Pierre
_________________________
Pierre Belarge
Top
#87199 - 02/01/04 08:01 AM Re: 680.22(A)(4)
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Thanks Pierre
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 85 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals