#87195 - 01/29/04 03:56 AM 680.22(A)(4)
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
i have a basement pool job. the gfi receptacle's furthest distance is 6' from the pool edge {which i'll feed via gfi breaker, as all the lighting switches are also there 680.22(B)(4)}

this was built this way, not an afterthought, just checking if i'm kosher here i guess...

680.22(A)(4) Restricted Space. Where a pool is within 3.0 m (10 ft) of a dwelling and the dimensions of the lot preclude meeting the required clearances, not more than one receptacle outlet shall be permitted if not less than 1.5 m (5 ft) measured horizontally from the inside wall of the pool.


HB commentary;

The receptacles within the structure are permitted to be less than 10 ft from the pool. Where this installation is at a dwelling unit, it is necessary to provide at least one receptacle between 10 ft and 20 ft from the inside walls of the pool

~S~
Top
2017 / 2014 NEC & Related Books and Study Guides
#87196 - 01/29/04 06:09 AM Re: 680.22(A)(4)
earlydean Offline
Member
Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
The commentary you quoted does not apply to the code section noted. If your lot precludes the receptacle from being installed between 10 and 20 feet from the pool, then it is permissible to install a receptacle between 5 and 10 feet to satisfy 680.22(A)(3).

Earl

I think (4) should be made a subsection of (3), as it applies only to that sub-section.
_________________________
Earl
Top
#87197 - 01/30/04 01:36 PM Re: 680.22(A)(4)
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
thanks Earl but....
Quote:
Where a pool is within 3.0 m (10 ft) of a dwelling and the dimensions of the lot

does this apply to inside a dwelling as well as outside?

~S~
Top
#87198 - 02/01/04 06:31 AM Re: 680.22(A)(4)
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
Sparky
That is a good question. My opinion is the restricted lot requirements would conform to this pool, but I am not your AHJ. I would ask him to be sure.

Pierre
_________________________
Pierre Belarge
Top
#87199 - 02/01/04 08:01 AM Re: 680.22(A)(4)
sparky Offline
Member
Registered: 10/18/00
Posts: 5545
Thanks Pierre
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
License exam
by TRUE POWER
Today at 09:16 PM
Looking for older post
by sparkyinak
Today at 12:27 AM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 74 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 03/13/07
Posts: 167

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals