The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 97 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87195 - 01/29/04 03:56 AM 680.22(A)(4)
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
i have a basement pool job. the gfi receptacle's furthest distance is 6' from the pool edge {which i'll feed via gfi breaker, as all the lighting switches are also there 680.22(B)(4)}

this was built this way, not an afterthought, just checking if i'm kosher here i guess...

680.22(A)(4) Restricted Space. Where a pool is within 3.0 m (10 ft) of a dwelling and the dimensions of the lot preclude meeting the required clearances, not more than one receptacle outlet shall be permitted if not less than 1.5 m (5 ft) measured horizontally from the inside wall of the pool.


HB commentary;

The receptacles within the structure are permitted to be less than 10 ft from the pool. Where this installation is at a dwelling unit, it is necessary to provide at least one receptacle between 10 ft and 20 ft from the inside walls of the pool

~S~

Top
2014 / 2011 NEC & Related Books and Study Guides
#87196 - 01/29/04 06:09 AM Re: 680.22(A)(4)
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
The commentary you quoted does not apply to the code section noted. If your lot precludes the receptacle from being installed between 10 and 20 feet from the pool, then it is permissible to install a receptacle between 5 and 10 feet to satisfy 680.22(A)(3).

Earl

I think (4) should be made a subsection of (3), as it applies only to that sub-section.
_________________________
Earl

Top
#87197 - 01/30/04 01:36 PM Re: 680.22(A)(4)
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
thanks Earl but....
 Quote:
Where a pool is within 3.0 m (10 ft) of a dwelling and the dimensions of the lot

does this apply to inside a dwelling as well as outside?

~S~

Top
#87198 - 02/01/04 06:31 AM Re: 680.22(A)(4)
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
Sparky
That is a good question. My opinion is the restricted lot requirements would conform to this pool, but I am not your AHJ. I would ask him to be sure.

Pierre
_________________________
Pierre Belarge

Top
#87199 - 02/01/04 08:01 AM Re: 680.22(A)(4)
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Thanks Pierre