The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 240 Guests and 3 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87180 - 01/28/04 02:49 PM Transformer secondary tap
bobwk Offline
Junior Member

Registered: 05/16/03
Posts: 6
Loc: baltimore
I am trying to design a tap ahead of a main breaker for a Hangar door, and NFPA 409 requires a tap ahead of the main. Can an indoor transformer, dry type, 13.2kV pri, 480V secondary be tapped inside the transformer cabinet with 600V insulation wire. Would the tap conductor be required to be rated 15 kV, the transformer is not compartmentalized and is unisulated bus bar on the 480 side to the switchboard. The transformer is up against the main breaker section, all customer owned and metering is not an issue. Any code references would be appreciated.

Top
2014 / 2011 NEC & Related Books and Study Guides
#87181 - 01/29/04 06:46 AM Re: Transformer secondary tap
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
NFPA 409:"5.7.2 The power source for hangar doors shall operate on independent circuits and shall not be deenergized when the main disconnect switches for general hangar power are shut off."
Seems to me you could set it up so that you won't have to connect ahead of the main. Why not have a main distribution panel fed by the transformer, one feeder would be to the general hanger panel, a second would go to the hanger doors panel.

Earl
_________________________
Earl

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals