The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 202 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#87138 - 01/25/04 11:34 AM barn or detached garage
Wirenuttt Offline
Member

Registered: 11/10/02
Posts: 267
Loc: Massachusetts
What are some of the requirements for installing a sub-panel in a detached garage as far as grounding is concerned? Is it just a 4-wire isolated netral at the sub panel? What about an additional ground rod? Have any of you done these installations and how did it go with the inspector?

~Andy

Top
2014 / 2011 NEC & Related Books and Study Guides
#87139 - 01/25/04 03:07 PM Re: barn or detached garage
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
if only one branch circuit is connected to the building, no ground rod is required.

Top
#87140 - 01/25/04 03:46 PM Re: barn or detached garage
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Two code options for running a feeder to a separate structure, both require ground rods and any other electrodes present to be used.

1)3 wire feeder with neutral bonded to ground at the added panel.

This method is only allowed if there are no continuous metallic paths bonded to the grounding system in both buildings or structures involved.

In other words no parallel paths for neutral current.

2)4 wire feed with isolated neutral bar and bonded grounding bar.

Look at 250.32(B)(1) and (2)
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#87141 - 01/28/04 02:08 PM Re: barn or detached garage
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
the 3 wire/4 wire argument goes round in circles with those opposed to 3 wire pointing to even acidic soil, and those that advocate it pointing to standard poco installs

the 'one circuit' exception forgoing the G-rod ends up inevitably w/3 ph multiwire circuits, or an OCPD as definitoinal benchmarks.

Top
#87142 - 01/28/04 05:35 PM Re: barn or detached garage
russ m Offline
Member

Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
Bob:

Is it your contention that this is a "feeder" going out to the garage, and not a branch circuit(multiwire), because it is fed from a circuit breaker that is not the final overcurrent device.
The final overcurrent device being the branch circuit breakers in the panel that's in the garage.

Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlets.

Russ

[This message has been edited by russ m (edited 01-28-2004).]

Top
#87143 - 01/28/04 05:50 PM Re: barn or detached garage
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Russ: The original post asked about installing a panel at a detatched structure. This would require that a FEEDER circuit be installed, since the panel contains OCPD's, not outlets.
_________________________
Ryan Jackson,
Salt Lake City

Top
#87144 - 01/28/04 06:08 PM Re: barn or detached garage
russ m Offline
Member

Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
Thanks Ryan

I was just try to word it so we all understood it, I was a bit confused at first.

Top
#87145 - 01/29/04 01:41 PM Re: barn or detached garage
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Thanks for the assist Ryan and yes that was what I was going for.

A single branch circuit including a multiwire branch circuit you could forget about the ground rod, I know I would.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#87146 - 01/29/04 01:43 PM Re: barn or detached garage
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Oh and if someone could explain the reason one circuit does not need a ground rod and two circuits require a ground rod I would really like to know.

Sparky, what have you heard for this?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#87147 - 01/29/04 03:00 PM Re: barn or detached garage
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
 Quote:
Sparky, what have you heard for this?


usually the converstaion turns to the technicalities of making a G-rod GEC onto a single pole switch...

at which point conceeding to the branch circuit exception seems reasonable

~S~

Top
Page 1 of 2 1 2 >