The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
01/19/17 09:52 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
2 registered (Ruben Rocha, gfretwell), 0 Guests and 187 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#87075 - 01/16/04 04:59 PM 4 - 1/0 IN 2inch LB
LK Offline
Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Can you put 4 - 1/0 in a 2" LB ?

Top
2017 / 2014 NEC & Related Books and Study Guides
#87076 - 01/16/04 05:54 PM Re: 4 - 1/0 IN 2inch LB
gserve Offline
Member

Registered: 03/11/03
Posts: 92
Look in the inside of the LB for max wire size and number

Top
#87077 - 01/16/04 07:01 PM Re: 4 - 1/0 IN 2inch LB
LK Offline
Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Max wire size is 4/0 as in all 2" LB's however max fill notes not more than 3 conductors, it seams for conductors over #4 three is the limit, fittings are not the same fill as conduit. This would prevent using 2" LB for 3PH Service LB.

[This message has been edited by LK (edited 01-16-2004).]

Top
#87078 - 01/17/04 04:55 PM Re: 4 - 1/0 IN 2inch LB
rizer Offline
Member

Registered: 01/03/04
Posts: 90
Loc: bradenton ,fl.,usa
you could always use a larger lb with reducing ends.

Top
#87079 - 01/17/04 05:46 PM Re: 4 - 1/0 IN 2inch LB
russ m Offline
Member

Registered: 02/22/03
Posts: 165
Loc: Burbank,IL,USA
314.28 Pull and Junction Boxes and Conduit bodies.(A)(2) would require more than a standard LB. It usually requires a mogul LB.

Top
#87080 - 01/17/04 06:00 PM Re: 4 - 1/0 IN 2inch LB
LK Offline
Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Russ,
You got it, I posted for one of my guys, He said there is nothing wrong with using a regular LB, he din't get a mogul because the supply house din't stock them, and if they had to order, it would cost more. I stopped the job and refuse to let them use the regular LB. Their answer is, we see everyone else use them, and is the inspector going to ask you to tear down the job. I don't want to take that chance.
Rizer,
The larger LB with a reducer will not meet the requirements of 314.28(A)(1), it is still to short in length. Only the Mogul LB will do it.

[This message has been edited by LK (edited 01-17-2004).]

Top
#87081 - 01/18/04 07:53 AM Re: 4 - 1/0 IN 2inch LB
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
LK,
Max 4/0, as with all 2" LBs?
I think you'd be better off to follow gserve's instruction, and look in the inside of the LB.
From the OZ/Gedney catalog:
LB-200A = Max 3 #4/0 AWG, (aluminum for rigid)
LB-67 = Max 3 #1/0 AWG, (a Form 7 LB)

I regularly see the use of 2" Appleton LB's (aluminum) Max 2/0 with 3/0 wire on 200 Amp circuits...S

[This message has been edited by electure (edited 01-18-2004).]

Top
#87082 - 01/18/04 10:18 AM Re: 4 - 1/0 IN 2inch LB
LK Offline
Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Electure,
Max 4/0, as with all 2" LBs? is the comment from one of my guys, that asked me to post this, He had a carlon LB 2" J type that has 4/0 stamped inside. He now knows that all LB's are not equal. style and type for different applications. They forget bending space and fill requirements when it comes to LB's. Yes you will see this violation many times.


[This message has been edited by LK (edited 01-18-2004).]

Top
#87083 - 01/18/04 01:41 PM Re: 4 - 1/0 IN 2inch LB
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Sorry and no offense, LK
I guess I didn't quite understand.
Another way to accomplish this (LB) in certain circumstances is to use a section of wireway with the required distance between conduit entry points. They're sure a lot less expensive, and more easily available than the mogul conduit bodies...S



[This message has been edited by electure (edited 01-18-2004).]

Top
#87084 - 01/18/04 06:13 PM Re: 4 - 1/0 IN 2inch LB
LK Offline
Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
electure,
We are doing a 200A 3 phase system next week, and I am using a box on the inside of the building, basement area, if I can find one with the proper gauge for service conductors. Still using mogul outside, you can guess what a 2-1/2" mogul LB costs. By the way, one of the guys called today and said he wanted to thank me for giving him the chance to be an electrician.

[This message has been edited by LK (edited 01-18-2004).]