ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 17
Recent Posts
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,476 Are you busy
166,184 Re: Forum
160,637 Need opinion
Who's Online Now
0 registered members (), 54 guests, and 13 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#86821 - 12/18/03 07:51 PM Is this requirement being enforced by any AHJ's?  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Is this requirement being enforced by any AHJ's?

Is this requirement being enforced by any AHJ's?

Quote
250.104(B) Other Metal Piping.

Where installed in or attached to a building or structure, metal piping system(s), including gas piping, that may become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used.

The bonding jumper(s) shall be sized in accordance with 250.122 using the rating of the circuit that may energize the piping system(s).

The equipment grounding conductor for the circuit that may energize the piping shall be permitted to serve as the bonding means.

The points of attachment of the bonding jumper(s) shall be accessible.

FPN:Bonding all piping and metal air ducts within the premises will provide additional safety.


Commentary:

Section 250.104(B) was revised for the 2002 Code to state that gas piping is treated exactly the same as all "other metal piping" systems within a building.

Quote

NFPA 54 - 6.13 Electrical Bonding and Grounding.

6.13.1 Each aboveground portion of a gas piping system that is likely to become energized shall be electrically continuous and bonded to an effective ground-fault current path.

"Gas piping shall be considered to be bonded when it is connected to gas utilization equipment that is connected to the equipment grounding conductor of the circuit supplying that equipment."

6.13.2 Gas piping shall not be used as a grounding conductor or electrode.


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#86822 - 12/18/03 08:45 PM Re: Is this requirement being enforced by any AHJ's?  
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
Yes sir. If I'm not mistaken, the '99 required gas piping to be bonded, but because the NEC used a referenced standard to require it, they couldn't change the wording of the reference (the national gas code?). I was very glad taht the 2002 spelled it out clearly. This is a good provision and should be enforced.


Ryan Jackson,
Salt Lake City

#86823 - 12/18/03 09:42 PM Re: Is this requirement being enforced by any AHJ's?  
Jim M  Offline
Member
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
The only one I know of in MD that will not allow this is Baltimore City. All the others I deal with require the gass to be bonded.

I had heard something a long time ago about someone not having a potential current flow thru the gas line, especially with any work being done that would break a joint, like around a gas meter.


#86824 - 12/18/03 10:45 PM Re: Is this requirement being enforced by any AHJ's?  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Joe,

Can we take this a little step farther, what about a piece of steel I-beam in a house? The whole house is built of wood studs, butthe main beam in the basement is a large steel I-beam. Most of the electrical wiring is running along side that beam in a chase. Would that I-beam need to be bonded to the electrical system?


#86825 - 12/18/03 10:49 PM Re: Is this requirement being enforced by any AHJ's?  
dana1028  Offline
Member
Joined: Jan 2002
Posts: 163
San Carlos, CA
My underderstanding of this 'gas piping likely to become energized' is this:

1. Gas piping likely to become energized will likely become 'energized' at an appliance utilizing the gas.

2. The mandatory EGC requirement for all circuits automatically bonds this equipment (and thus the gas piping associated with it).

3. Thus, no additional bonding is required...i.e. as it is already bonded through the EGC.


#86826 - 12/19/03 12:00 AM Re: Is this requirement being enforced by any AHJ's?  
golf junkie  Offline
Member
Joined: Apr 2001
Posts: 507
York, NE
This is not being enforced in Nebraska.

GJ


#86827 - 12/19/03 02:53 AM Re: Is this requirement being enforced by any AHJ's?  
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
Actually this is complied with when you hook up the bare or green ground wire to the equipment ground screw. for example in the furnace or hot water heater.

[This message has been edited by nesparky (edited 12-21-2003).]


ed

#86828 - 12/19/03 06:59 AM Re: Is this requirement being enforced by any AHJ's?  
zapped208  Offline
Member
Joined: Feb 2003
Posts: 196
Somewhere in USA
Not in my area either.


Shoot first, apologize later.....maybe

#86829 - 12/19/03 08:10 AM Re: Is this requirement being enforced by any AHJ's?  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Phila., PA area inspection agencies require it. As does the local utility.


#86830 - 12/19/03 08:28 AM Re: Is this requirement being enforced by any AHJ's?  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
Quote
Is this requirement being enforced by any AHJ's?


no Joe, it is being 'enforced' by me,

Steve (aka, if it don't move ground it) sparky


Page 1 of 2 1 2

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.8162 MB (Peak: 0.9899 MB) Zlib enabled. Server Time: 2017-03-26 07:19:42 UTC